How can we calibrate the level interface for Fisher®
FIELDVUE® DLC3000?if use water to calibrate and our liquid
SG are 0.75 and 1 ,Displacer height=14" and How much should
be set SG in trasmitter during calibrate,for URV and LRV
how shold be set
Answer / iit
Calculation # If the calibrating liquid is water:
In the DLC3000 (Need Hart to communicate)
-ON Basic set up_PV set up set PV is Level
-ON Basic set up_PV set up set Specific Gravity =1
-ON Basic set up_PV set up_PV Rang set URV=14"and LRV=0".
1. First close both the primary isolation valves and drain
the liquid inside the chamber.
2. Fill water up to the center of lower flange level =0"
=0%
2.1 At DLC3000 on Basi set up_Sensor calibrate_Two Liquid
Lvl cal select Lower cal to get 0" =0% output
3. Fill it up to the center of the top flange level =14"
=100%
3.1 At DLC3000 on Basi set up_Sensor calibrate_Two Liquid
Lvl Cal select Upper cal to get 14" =100% output.
4. Fill it up to 50 %, check linearity.
After calibration completed with water and back on service
for interface
On DLC3000
-ON Basic set up_PV set up set PV is Interface
-ON Basic set up_PV set up set upper SG is 0.75,Lower SH=1.0
-ON Basic set up_PV set up_PV Rang set URV=14"and LRV=0".
and close drain valve and open both the primary isolation
valves unit ready to in service
| Is This Answer Correct ? | 8 Yes | 5 No |
wt is cold junction compensation
What is the constant voltage unit?
Explain signal isolator
Tr. Wiring for calibration.
uses of profibus?
How many problems can be occurring in solenoid valve? And how it can be rectified?
if we open the inlet of an air regulator ,how it will affect the out put of regulator? (out put of regulator is using to operate an on-off valve.it is an air to open valve,and valve is in open position.my doubt is air regulator will hold the valve in open or not,if there is no consumption or leak in regulator out put side ,we only loose the input pressure.)
what is solenoid valve?
What is the difference between intrinsic instruments and ATEX instruments?
What are continuances of connecting earthing and shield of branch cables (instrument to Junction box), at the same earthing pot provided on JB? Is it ok, or may produce some problem?
0 Answers Process Control Technologies,
DEAR SIR/MADAM MY NAME IS ARKAPROVA BHATTACHARYYA.I AM A FRESHER INSTRUMENTATION ENGINEER.CAN YOU PLEASE SEND SOME QUESTION PAPERS OF GRADUATE ENGINEER TRAINEE EXAM OF DVC(DAMODAR VALLY CORPORATION).MY EMAIL IDs ARE arka_aec@rediffmail.com.
What is require for PLC Programming?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)