how hazordious area is classified at an oil & gas plant
and categorise suitable class of electric equipment in that
area like induction motors, LCS, Lighting Fixtures
Fluerescent/Flood lights Mercury& sodium lights, J.Bs,
Power Cables etc
Answers were Sorted based on User's Feedback
Hazourdous areas are clasified according to the process of
the plant in a Oil or a gas plant dipends upon the lekages
like gasses or oils where occur in a work place
there are 3 zones
1. zone - 1 where lekages of oil or gas occur in abnormal
conditions
2. Zone - 2 where lekages are never occur in normal
conditions
3. Zone - 0 where lekages are likely occur in normal
operation conditions
the usage of electrical equipment is EXD EXP EXE
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / b das
For zone-0 ; no electrical equipment
For zone-1 ; only flame proof(FLP) electrical equipment
including cable gland with witht mark "exd","exp" "exi"
(intrinsically safe for instruments)certified by CMRI
For zone-2 ; electrical equipment including cable gland
with mark "exe" but continuous sparking part eg. slipring
etc. enclosure must be "exd"
Apart from above there are again gas group;1A,IIA/IIB,IIC.
Area under IIC most hazordous.
| Is This Answer Correct ? | 4 Yes | 0 No |
What is on delay and off delay timers
i need online ups battery calculater
i need to calulate the cable size when watts are mentaind wat z the formula
how hazordious area is classified at an oil & gas plant and categorise suitable class of electric equipment in that area like induction motors, LCS, Lighting Fixtures Fluerescent/Flood lights Mercury& sodium lights, J.Bs, Power Cables etc
Dear Respected sir how to test ABB REX521 protection relay by relay tester.
How would your past experience translate into success in this job?
what is the function of a circuit breaker ?how does the circuit breaker function during normal operation of an electrical system
How will polarity test of Dy5 transformer ?
In Dyn11 power transformer if any one of the 3 phases connected to earth in star connected side then please explain effect of the current flow in delta connected side of transformer.(In this case if one phase is shorted to ground in star connected side then we observe the current flow in two phases only not three phases in delta connected primary side. Please explain why it is so?)
we convert 66kv to 33 kv to 11kv to 440v. why can't we directly convert 33kv to 440 ?
What are the disadvantages of LT AVR over HT AVR?
1 Answers APTransco, Jindal, TNEB Tamil Nadu Electricity Board,
is it possible to start a motor in felid connected to a remote mcc
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)