how to connect generators in parallel and what are the
required equipment to do so?
Answer Posted / bijulal
for the two generators connected in parallel the following
conditions:
voltage of both machine will be same
frequency must be same
phase sequence must be same
the equipments are:voltmeter,ammeter,wattmeter,
synchronuscope& reverse current relay will be
used.
| Is This Answer Correct ? | 10 Yes | 3 No |
Post New Answer View All Answers
What are the types of class b amplifier?
What is the difference between UPS & inverter ? which UPS is better and whos got the edge ? what is the difference between & inverter ? which UPS is better and whos got the edge 12 V , 24 V , 36 V etc what are the advantages of 12 V, 24 V , 36 V etc and what are the disadvantages of 12 V, 24 V, 36 V etc thanks
My load is 1635 KW. & current pf is 0.884, I have to improve it for 0.99.Please suggest what KVAR value is needed?
what is KA rating and how can we choose switchgears on applications
What tests should i carry over on a newly rewinded DC Generator with voltage rating of 38 volts and current rating of 350 amps, to certify that the machine is OK?
why is using sensor?what is differece between photoelectric and proxmitty?
how to calculate the step resistance for slipring induction motor,how you deside the no of step for that?
What is shutdown of electrical sub station?
what are the main faults that occur in stabilizers? How they corrected and resolved ? Types of stabilizers ?
how can we design robots
How do I calculate a WTI CT ofa 1250kVA 6600/400V transformer
write circuit diagram for a motor rotate in forward direction once it started and when pressed the same button it should rotate in anticlockwise.
Hello sir i m student of gtu .what is idp.
3ph motor running with unequal kw and different pf what are the reasons
Give some example of fault limiting devices?