If my sfu is 64 Amp & its link is 32 Amp then at what
amp.my sfu will trip???
Answers were Sorted based on User's Feedback
Your link is 32 Amps so if any more than that specified
32Amps current occurred means then the fuse link will trip
i.e. its blown out that fuse wire.
That 64Amps is mentioned the Switch Fuse Unit(SFU) withstand
capability.i.e. that SFU Unit can withstand upto 64Amps.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / k.prakashchandra
In sfu there is no tripping mechanism generally. Tripping
takes place at the set value.The link may sustain 64 A for
a short period if the cont capacity is 32 A
| Is This Answer Correct ? | 0 Yes | 0 No |
What is electrical grounding?
What is Single Phasing fault???(not single-phase fault)
can i use the six sigma method which is used in management area, in state estimation of power systems?
why three phase three wire system probably did'nt have neutral
one 60KVA UPS how can full load current tell me us formulas
Why inductors are installed in electrical circuits?
we are operationing 3NOs 800 Kva generators by singronyus.specialey evening time our panel trip. the panel showing generator earth fault
how to calculate the megger values for motor, cables and transformers?
what is stator inter turn fault?
how to find out this one mcb r mccb?
what happen when power factor of 2 parallely operated transformer become equle?
WHERE IS THE LIGHTING ARRESTER SHOULD BE PLACED IN DISTRIBUTION LINES?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)