what do you mean by earth fault in transformer?
Answers were Sorted based on User's Feedback
Answer / shailesh aggarwal
Basically Earth faults are caused if high fault current
flows through the neutral of the transformers. This type of
fault arises mainly in Star connected transformers.Earth
faults are specified in many categories:
1. Restricted Earth faults(Inside the zone HT/LT side of
trafo) Connection are done b/t Phase CT & Neutral CT of
tranformer)Indicated as REF(64)
2. Standby Earth Faults(Directly linked with neutral of
trafo)connection only done b/t neutral CT.Indicated as SBEF
(51N).
Both the protection give signals to the numerical relays
and cause the tripping as earth faults and directly trip
the transformer.
Thus in order to save transformers a proper earthing is
required whether solid or usong NGRs.
| Is This Answer Correct ? | 22 Yes | 2 No |
Answer / nilkanth tailor
EARTH FAULT REQUIRE C.T.(CURRENT TRANSFORMER)..TO SENSES
IMBALANCE IN 3 PHASE..GENERALLY 3PHASE SYSTEM IS IN BALANCE
CKT...IF SINGLE OR MULTI PHASE WAS EARTHED..AND AT THAT
TIME IMBALANCE PRODUCED..CT WILL BE DETECT FAULT CURRENT
AND CIRCUIT BREAKER WILL BE OPEN...THATS CALLED EARTH FAULT
PROTECTION OF X'MER...
| Is This Answer Correct ? | 9 Yes | 6 No |
what is the use of surge suppresser in 33 KV incoming panel. where it must be installed,inseries with incoming cable surge suppresser must be at incoming of the breaker are outgoing of the breaker
how to carry out Magnetizing Current Test on Distribution transformer and what purpose we are doing this test.
can any one suggest websites having study maetrials for the electrical students?
What is the unit of attenuation?
I am applying for NTPC examination.Can we please provide previous paper to my mail prasad.chintala108340@gmail.com
What is the importance of quality factor in resonance?
Where -48 volt DC use & why?????????
10 Answers Ericsson, INDUS, Indus Towers, Telecom,
how to calculte capacitor range for single phase induction motors??pls tel
How over load relay works.
At site, we have 30Kw motor (3 phase, 400V,50Hz) and FLC 54A as per the nameplate. At the time of starting it draws 840A instead of 390A (7.2%). As per the data sheet also its 390A starting current. it thru a dol starter from the MCC. can anyone tell what is the problem in the motor
why autotransformers are not safe for supplying low voltage from a high voltage source?
why conductors of low tensile strength 1)produce greater sag and 2)can not be used for larger spans
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)