Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate the size of the cable? for exp i want to
use the load of 10HP

Answers were Sorted based on User's Feedback



How to calculate the size of the cable? for exp i want to use the load of 10HP..

Answer / bala.a

Hai
its is very simple
load=10 HP
10 X 0.746= 7.46 KW

7.46 X 1000/ ROOT 3 X 0.8X 415= 12.97 A= 13 A

So our require cable shouls be withstand 13 A AT full load
condition .

u will reff any one cable manufacture catalouge which
cable suitable for the same load . but that cable to be
suitable for Appx -18A because u will consider the
derating factor for cable .

Is This Answer Correct ?    6 Yes 1 No

How to calculate the size of the cable? for exp i want to use the load of 10HP..

Answer / santosh

Sqmm of cable depends upon the cable material.In thumb rule Cu cable can carry 10-12 times of its rated sqmm.For ex 10 sqmm cu cable carry 100-120 amps.Al cable carry 4 times current of its rated sqmm

For ur problem: 13A is rated current. 50-60 amp staring current,7-8 running cu.So u may need 4 sqmm Al cable or 2.5 sqmm cu cable.

Is This Answer Correct ?    0 Yes 0 No

How to calculate the size of the cable? for exp i want to use the load of 10HP..

Answer / anil

Sir, it is simple 10kw motor will take 14 amp current in
normal running of motor but at starting shall take about 5-7
times more in case of induction motor. so we will consider
the cable accordingly

Is This Answer Correct ?    2 Yes 3 No

How to calculate the size of the cable? for exp i want to use the load of 10HP..

Answer / charan

fine buddy, what i want is how the manufactures is deciding
that Sqmm of the cable ??

Is This Answer Correct ?    0 Yes 6 No

Post New Answer

More Electrical Engineering Interview Questions

how much rating of fuse and MCB should be used for a load consisting of 6KW and 18KW inductive load?

1 Answers  


Control cables in S's will carry 1000v which is AC R DC? Pls answer me 

0 Answers  


1. A 380 / 220 V r.m.s. 3-phase 4-wire circuit carries loads of 8 + j8.1 ohm; 4 + j4.1 ohm; and 2 +j2.1 ohmin the three phases respectively. The length of the circuit is 100 m, and the resistivity of the phase conductors is 0.0005 Ω/m. The neutral conductor is of the same size as the phase conductors. a) Select a reference angle 0for the first phase. Then write down the three phase voltages in both polar format and complex number format. b) Make appropriate assumptions, and take temperature effects on resistance is insignificant. Calculate the currents in the three phases. (Note: Determine conductor resistance, and apply Kirchhoff’s Voltage Law) Based on the result, suggest a main switch rating for the circuit. c) Show your preferred direction of neutral current in a diagram, and then determine its value. (Note: Apply superposition principle, and Kirchhoff’s Current Law) Use its magnitude to show that in this circuit, the unbalanced load may increase the voltage drop in some of the phases. (Note: Also observe the common volt drip in neutral) State your assumptions, if there are any. d) Suddenly the neutral wire of the circuit is broken. Estimate the new currents in the first phase, i.e. Phase L1. State your assumptions, if there are any.

0 Answers  


why fault current always calculated for 1 seconds?

3 Answers   Coca Cola,


How can calculate ups battery back up time?

25 Answers   Cisco, Cooper, Pronet, Wipro,


What are the tests carried out on transformer while testing at sites?..Pls explain me in detail

2 Answers   Suzlon,


what is meaning of AMF, WHY IS USING IN GENSET

1 Answers  


what is the difference between star and delta connection ? when we use each one ?what is the best ?

14 Answers   Amara Raja, Daikin,


what is the formula of starting current of 3phase and 1 phase motor???

0 Answers  


what is the std. earthing resistance for 440V system or m/c, 33000/440 Volt substation? What is the std.?

2 Answers  


If 440 V supply has given at the secondary winding of transformer at that time if we apply 11 KV at primery then what will happen???????

4 Answers  


WHAT IS LIGHTNING,HOW TO CALCULATE LIGHTNING DESIGN CALCULATION?

2 Answers   L&T,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)