what is the use of neutral displacement relay
Answer / loboreliance2003
The relay comprises an attracted armature element fed via a
rectifier and series resistor. It can be provided with
either a fixed
setting, or variable settings using a plug bridge. It has a
minimum
withstand of rated voltage continuously.
Operation of Neutral Voltage Displacement Relays
The zero sequence current that flows for an earth-fault on
an un-earthed network is determined by the capacitance of
the cable to earth. This flow of current leads to a rise in
the voltage of the neutral point of the incoming supply
(the star-point of either the generator or transformer). It
is this rise that is detected by a neutral voltage
displacement relay. If the network is quite small (i.e.
short cables), then the zero-sequence voltage will be
unstable. This is why an instantaneous relay is only
generally used to provide an alarm. In the event of a
fault, neutral voltage protection cannot detect the
location of a fault, so all sources of supply should be
disconnected.
Is This Answer Correct ? | 10 Yes | 9 No |
if power factor comes in leading & showing -0.95. Is there any effect on electrical system? if yes, then please tell me what would be the effects. & how long we keep power factor in leading. Keeping power factor in leading shows more KW & less KVA is it correct or not.
why is fan rotating slow speed, what is the problem?
If we need 4c× 50mm sq cable but it's not available so we can pull 4c×25mm sq two cables?
why the star delta motors burn out frequently
What is Diff btw Fire Alarm & VESDA System???
why it is unable to birds to be on a 220kV 0r 132 kv lines like on 33kV and 11kV lines?
4 Answers MSETCL Maharashtra State Electricity Transmission Co Ltd,
Hi everyone. Some Generators uses 3-Pole breakers with extra contactors for Neutral. Some uses 4-Pole. Why so? What is the idea behind this? Thanks in advance for the solution. Kr.
Can RCD's used to protect the VVVF drive if not why.
Need help. 3 phase system. Neutral line arced and melted upon connection of connector with 3 phase power. Why would that happen?
Dear sir, I have completed DECE in the year 1995. I have work experience in HT and LT LINE more than five years. Now i am doing BE in EEE from rajasthan university. After completion of BE,can i apply "C" Licence sir? Please reply.
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a campus site?
how to get electrical supervisor competency certificate in gujarat. i did 3 year diploma in electrical