two transformers are separated by concreted wall becuase of
when any fault occurs which results in fire on any one of
transformer it protects the healthyone transformer.
| Is This Answer Correct ? | 8 Yes | 1 No |
Answer / guru
If the distance between the transformers is more than the
requirement then firewall will not be required as per IER
1956 standards.
There is a minimum distance laid down in IEC1956 based on
the capacity, voltage rating of the transformers
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / tom hanks
Any two transformers in a plant/substation are always
seperated by a concrete wall known as BLAST WALL, (Blast
walls are generally 1000mm+ bigger the size of larger
transformer) It is protect the healthy transformer from
fire, incase the other one is on fire due to short-
circuit/oil leakage etc.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / shaji samuel
Two Transformers aside should be supperated by concreted
wall because through blast wall we prevent the two
transformers with each other fault,shortcircuit sparks, and
due to the blast of the oil tank of the transformer then we
can prevent the safe one transformer.
| Is This Answer Correct ? | 3 Yes | 0 No |
It is fire wall, during fault condition if transformer at
fire it should not spread to other equipment/buildings.
As per IS, the thickness should be 350mm brick wall/230mm
concrete wall. Height of the wall shall be decided based on
the height of x'frm
| Is This Answer Correct ? | 2 Yes | 0 No |
Why Neutral Busbar CT & transformer neutral CT connected with phase CT in Restricted Earth Fault?
what happen as when voltage drop(or may decrease) ? in case of atomic base theory?
how are reversing the direction of dc motor
What is double delta conection in AC Motor? And can we done the double RPM of the motor by double delta conection?
is all the servo motors having brake?please specify which servo motors having brake for stop on position and which are not.
what are the protection equipments used betbeen HT line and transformer in a power plant
what is the mechanical safety of DG ?
Why r use in the tap changing x' mer.
what is surge suppressor?
i want to make an elec generater with only 12v car battery car alternater and 12 volt motor ..... will the battery charge and give power at same time with out over charging the battery?
Define demand factor?
what diferent amoung three phase supply?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)