Answer / sanjeev nair
The formula for calculating the Capacitive kVAr required to
compensate inductive kVAr is kW*sqrt(tan_angle1-tan_angle2).
In your case, you have to check the present power factor
and then the kW.
Suppose, If you have load of 50kW and the power factor is
0.8 and you have a plan to improve the PF to 0.95 then as
per the above formula the Capactive kVAr required to
compensate the inductive kVAr would be 21.
Besides, one should understand and work on the application.
ie, you can go for a 20 kVAr capacitor bank as per the
above if you have 50kW motor working on a pf of 0.8. If
both load and inductive kVAr is varying, then you have to
go for automatic pf control system with suitable banks to
compensate the inductive kVAr.
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / chiknabacha
http://www.newindiaelectricals.com/newindia/exports/capacitor/calculation.htm
Please find the calculation for KVAR from the required table
Is This Answer Correct ? | 0 Yes | 0 No |
what is the deference between watt and KVA
This is urgent!! What is a Thyristor-based 3-ways selector switch with Zero crossing control? how does it operate and where is it mostly found in a system?
how you will decide the distance between the power transformer and its fencing
what is the difference between series and shunt compensation using facts in a transmission line
8 Answers College School Exams Tests, Genco,
Define the term Capacitance and Inductance?
what is the function of starter & choke in the tube light set & how choke give 1000 volts while switching on.
14 Answers ADNOC Abu Dhabi National Oil Company, IBM,
What is the meaning of high reputuring in HRC fuse.?
Can we use shunt trip coil instead of trip coil with protection relay for protection?
what is the difference between Power and Distribution transformers ?
1 HP = how many Kva
What happen if field ckt is open when a sailent pole alternator connected to infinite bus
What is the role of Dedicated earthing in UPS System?