present we are having 0.8pf but I want increase it up to
0.99 so what is the formula for it and how can i calculate?
Answers were Sorted based on User's Feedback
Answer / kuppuswamy
PF = KW/KVA That is power factor = True power divided by
Apparent power.
If you want to increase the PF in generator, you have to
adjust the speed and voltage to bring to the required PF.
If you want to increase PF in industrial load, you have to
go for adding the capacitor banks in the line side.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / satheeshramesh
If u wish to increase the P.F from 0.8 to 0.99 u have to
add capacitor banks.
Capacitor rating required (kVAR) =kW(tanØ1-tanØ2)
Cos Ø1 = 0.8, Ø1 = cos-1 (0.8), tan Ø1 = .
Cos Ø2 = 0.99, Ø2 = cos-1 (0.99),tan Ø2 = .
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / at
if you want to increase the power factor from 0.8 to 0.99
then in that case for
1. Generators:- you will have to increase the excitation
when generator is connected in an interconnected system
i.e. Many generators operating in parallel / or connected
to grid. increasing the excitation gives a leading power
factor and under excited generated draws lagging power
factor power.
2. When it is the case of Industries or other utilities
consuming electrical energy. one should know that all loads
consuming power are 99.99% inductive loads.Thus by adding a
capacitor bank of suitable rating shall be required to
compensate the lagging power factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
what happens when power factor leads or lags to electical or home appliances
Why the wave trap is put in Y phse only in switchyard?why not in other phases?
1 Answers IAG Automation, REL,
how to calculate the step resistance for slipring induction motor,how you deside the no of step for that?
Explain mechanical rotational system?
what is meant by negative conductor?
How to calculate phase to phase difference in 33KV Line ,11KV Line etc.
what is intermediate switch
What are options used for earthing the switchgear.
What are the safeties in elevators?what is the use of governor in elevator?
If any cable burnt how can we identify it burnt by high current of high voltage?
Where can I get CPWD electrical shedule rates in web? please help me.
why does a dc machine has high efficiency while working as a generator than as a motor
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)