present we are having 0.8pf but I want increase it up to
0.99 so what is the formula for it and how can i calculate?
Answers were Sorted based on User's Feedback
Answer / kuppuswamy
PF = KW/KVA That is power factor = True power divided by
Apparent power.
If you want to increase the PF in generator, you have to
adjust the speed and voltage to bring to the required PF.
If you want to increase PF in industrial load, you have to
go for adding the capacitor banks in the line side.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / satheeshramesh
If u wish to increase the P.F from 0.8 to 0.99 u have to
add capacitor banks.
Capacitor rating required (kVAR) =kW(tanØ1-tanØ2)
Cos Ø1 = 0.8, Ø1 = cos-1 (0.8), tan Ø1 = .
Cos Ø2 = 0.99, Ø2 = cos-1 (0.99),tan Ø2 = .
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / at
if you want to increase the power factor from 0.8 to 0.99
then in that case for
1. Generators:- you will have to increase the excitation
when generator is connected in an interconnected system
i.e. Many generators operating in parallel / or connected
to grid. increasing the excitation gives a leading power
factor and under excited generated draws lagging power
factor power.
2. When it is the case of Industries or other utilities
consuming electrical energy. one should know that all loads
consuming power are 99.99% inductive loads.Thus by adding a
capacitor bank of suitable rating shall be required to
compensate the lagging power factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
in a solar power plant,we are going to step up the voltage 350V to 33kv, and to 132kv GSS. i want to ask that if it is possible that 315v/33kv is not possible because we also use 315v/11kv. or it should be 415v/33kv? is it effects generation or losses? the second question is-generation is depends on LV winding? or LV winding design for generation voltage?
What are marginally stable systems?
how DC motor operating in detail .pls any one guide me .iam not clear idea about that .thank u
Why MCCB is Getting tripped sometimes when there is no load in the Midnight ?
why breaker closing coil gets burnt if supply is continously provided to it.
Two alternators say 1 & 2 are poised to parallel operation. But at the time of paralleing alternator 2 gets out of the system by tripping Earth fault relay. Please send me reply why this is happening?
My question is whether bellow formula is correct to find bus size for 46kA for 0.5 second & what is RT in bellow formula. formula to calculate the size of busbar to withstand the thermal stresses due to currents with duration of 0.2 sec to 5 sec. Sp = RT( I x I x t) / K Where Sp – is the cross sectional area of bus bar in millimeters. I - is the value of AC fault current. t - is the operating time of disconnecting device in seconds. K – is the factor depending on the material of the conductor, insulation and initial and final temperature. Value of ‘k’ for copper is 143.
can we use 220 volt 15 w a.c. lamp on 220 volt d.c.
How to do the meggering for a cable.
How we find the size of cable if we know the current
How to calculate amount of copper used in a motor (AC&DC), generator and transformer? Datasheet provides power rating and mass of the equipment....can we somehow use this available info.
how to setting Load amps tripping time and extra settings for load Transformer protection relay with RMU panel using C&S model relay..?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)