Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


present we are having 0.8pf but I want increase it up to
0.99 so what is the formula for it and how can i calculate?

Answers were Sorted based on User's Feedback



present we are having 0.8pf but I want increase it up to 0.99 so what is the formula for it and how..

Answer / kuppuswamy

PF = KW/KVA That is power factor = True power divided by
Apparent power.
If you want to increase the PF in generator, you have to
adjust the speed and voltage to bring to the required PF.
If you want to increase PF in industrial load, you have to
go for adding the capacitor banks in the line side.

Is This Answer Correct ?    7 Yes 0 No

present we are having 0.8pf but I want increase it up to 0.99 so what is the formula for it and how..

Answer / satheeshramesh

If u wish to increase the P.F from 0.8 to 0.99 u have to
add capacitor banks.
Capacitor rating required (kVAR) =kW(tanØ1-tanØ2)

Cos Ø1 = 0.8, Ø1 = cos-1 (0.8), tan Ø1 = .
Cos Ø2 = 0.99, Ø2 = cos-1 (0.99),tan Ø2 = .

Is This Answer Correct ?    7 Yes 0 No

present we are having 0.8pf but I want increase it up to 0.99 so what is the formula for it and how..

Answer / at

if you want to increase the power factor from 0.8 to 0.99
then in that case for

1. Generators:- you will have to increase the excitation
when generator is connected in an interconnected system
i.e. Many generators operating in parallel / or connected
to grid. increasing the excitation gives a leading power
factor and under excited generated draws lagging power
factor power.

2. When it is the case of Industries or other utilities
consuming electrical energy. one should know that all loads
consuming power are 99.99% inductive loads.Thus by adding a
capacitor bank of suitable rating shall be required to
compensate the lagging power factor.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

in a solar power plant,we are going to step up the voltage 350V to 33kv, and to 132kv GSS. i want to ask that if it is possible that 315v/33kv is not possible because we also use 315v/11kv. or it should be 415v/33kv? is it effects generation or losses?  the second question is-generation is depends on LV winding? or LV winding design for generation voltage?

0 Answers  


What are marginally stable systems?

0 Answers  


how DC motor operating in detail .pls any one guide me .iam not clear idea about that .thank u

2 Answers  


Why MCCB is Getting tripped sometimes when there is no load in the Midnight ?

0 Answers  


why breaker closing coil gets burnt if supply is continously provided to it.

1 Answers   TATA,


Two alternators say 1 & 2 are poised to parallel operation. But at the time of paralleing alternator 2 gets out of the system by tripping Earth fault relay. Please send me reply why this is happening?

2 Answers  


My question is whether bellow formula is correct to find bus size for 46kA for 0.5 second & what is RT in bellow formula. formula to calculate the size of busbar to withstand the thermal stresses due to currents with duration of 0.2 sec to 5 sec. Sp = RT( I x I x t) / K Where Sp – is the cross sectional area of bus bar in millimeters. I -    is the value of AC fault current. t -    is the operating time of disconnecting device in seconds. K –  is the factor depending on the material of the conductor, insulation and initial and final temperature. Value of ‘k’ for copper is 143.

0 Answers   Premier,


can we use 220 volt 15 w a.c. lamp on 220 volt d.c.

6 Answers   TCL,


How to do the meggering for a cable.

6 Answers  


How we find the size of cable if we know the current

2 Answers   Gemscab,


How to calculate amount of copper used in a motor (AC&DC), generator and transformer? Datasheet provides power rating and mass of the equipment....can we somehow use this available info.

1 Answers  


how to setting Load amps tripping time and extra settings for load Transformer protection relay with RMU panel using C&S model relay..?

0 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)