present we are having 0.8pf but I want increase it up to
0.99 so what is the formula for it and how can i calculate?
Answers were Sorted based on User's Feedback
Answer / kuppuswamy
PF = KW/KVA That is power factor = True power divided by
Apparent power.
If you want to increase the PF in generator, you have to
adjust the speed and voltage to bring to the required PF.
If you want to increase PF in industrial load, you have to
go for adding the capacitor banks in the line side.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / satheeshramesh
If u wish to increase the P.F from 0.8 to 0.99 u have to
add capacitor banks.
Capacitor rating required (kVAR) =kW(tanØ1-tanØ2)
Cos Ø1 = 0.8, Ø1 = cos-1 (0.8), tan Ø1 = .
Cos Ø2 = 0.99, Ø2 = cos-1 (0.99),tan Ø2 = .
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / at
if you want to increase the power factor from 0.8 to 0.99
then in that case for
1. Generators:- you will have to increase the excitation
when generator is connected in an interconnected system
i.e. Many generators operating in parallel / or connected
to grid. increasing the excitation gives a leading power
factor and under excited generated draws lagging power
factor power.
2. When it is the case of Industries or other utilities
consuming electrical energy. one should know that all loads
consuming power are 99.99% inductive loads.Thus by adding a
capacitor bank of suitable rating shall be required to
compensate the lagging power factor.
| Is This Answer Correct ? | 1 Yes | 0 No |
What will be the voltage regulation of a full load and 0.80 power factor lagging load transformer when a two winding single phase transformer has a voltage regulation of 4.5% at full load and unity power factor?
can we connect 2.2kw star motor in delta passion?
What is the 415V AC Soft starter? Explain with an example?
HOW TO CALCULATE THE HEAT AND LOAD OF LT-SUBSTATION WHICH CONTAINS 2*1MVA TRANSFORMERS,LT SWITCH BOARD,MLDB,ACB,BUSBAR,ETC...?
whats the differece between Exd and Exe
how to test reverse power trip?
explain single phase series motor
I have a 3 phase 600 volt prim. feed and a 120/208 sec. Isolateing tranformer .We are using this system for safety against shock . What is the proper grounding ?? Does the common on sec. get earth ground ???
we can use airconditioner for cooling the winding of transformer ,if not why?
what is the main difference b/w contactor and relay
2 Answers Pace Pharmaceuticals,
why we have and use 3 phase not 2 or 4 or other in power system?
how much amps will get from a 360/11kv line
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)