present we are having 0.8pf but I want increase it up to
0.99 so what is the formula for it and how can i calculate?
Answer Posted / kuppuswamy
PF = KW/KVA That is power factor = True power divided by
Apparent power.
If you want to increase the PF in generator, you have to
adjust the speed and voltage to bring to the required PF.
If you want to increase PF in industrial load, you have to
go for adding the capacitor banks in the line side.
| Is This Answer Correct ? | 7 Yes | 0 No |
Post New Answer View All Answers
How does the slip regulator works as a startor
How is the speed of a DC shunt motor related to the armature current?
which phase is preferred for connecting 1 phase vt used for synchronizing OHL? WHY?
How efficiency of thermal plant can be improved?
What is the difference between Delta & Wye windings?
What are chief characteristics of state-space method and its techniques ?
How to calculate the no of Ceiling fan (1200mm sweep) per unit area?
Define what is power quality meter ?
Ratings of power transformer,Distribution transformer.
Whether 3 phase induction motorwith 100 hp capacity , Amp 160 for which sensitive earth fault relay , type CTUM 15 can be used?
HOW CAN I GET 5CORE HO7 CABLE SIZE IF I HAVE 1800A?
how to estimate wiring ins roughing ins. and boxes
anyone knows service engineer in chennai for EDM SPARKING MACHINE.CHMER PULSE CD 60 M.pL GIVE ANY CONTACT NOS
What is Scheme Test of High Voltage Switchgear. Which tests it includes.
Is there any type of starter for DC motor other than two point,Three point and Four point starters?