Answer / vaibhav
yes we can drive the 50Hz motor on 100Hz by using variable frequency . and as we know that synchronous speed =120*f/p.
as frequency increase motor speed also increase. and also if frequency increase motor size also can be decrease in design if want to decrease
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / zenat
it will effect the motor speed,everything will run
(100-50)*100/50=100% faster than normal speed...which may
damage the motor.
| Is This Answer Correct ? | 3 Yes | 1 No |
Answer / clinton
If you are using a inverter on a 50Hz motor.
At 50Hz the VSD is usually outputing 400V
If the motor is connected in star the volage across each
coil is 230V at 50Hz. The motor will run with designed
magnetising current therefore can produce the correct
torque, then the load is increase. If we continue in
frequence, the magnetising current is lower, and therefore
the motor will loose torque.
Connect the motor in delta and change the settings to 415V
at 100Hz and the same magnetising curve is produced.
Therefore the motor will not stall due to lower torque
charactistics.
| Is This Answer Correct ? | 0 Yes | 0 No |
what is second harmonic, how is effect transformer ?.
what is the formula to calculate kva genset required for a given load in kw.
WHAT IS THE USE OF PIG TAIL IN WINDOW CT ?
Why there are some equipment(i.e:TV) that using 2-pin plug instead of three? What happen if there is current leakage? Are we going to get electric shock??
0 Answers College School Exams Tests,
What is the difference between switch gear and control gear ?
How many percent of power are not being registered if we bypass one side of the meter base terminal using #8 cu wire on 1-phase kwhr meter.
Why temperature rise test is conducted in bus bars and Isolators?
when motor taking high amp what happen.
How does a star connection and delta connection work? How does the star connection save starting current and how does it change to delta?
why DOL starter is use in induction motor as it is not reduce the starting torque
What will be MF if we have CT ratio is 130 of 3 nos?
how to calculate earth fault relay current and CBCT ratio
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)