HOW DOES THE PERCENTAGE DIFFERENTIAL PROTECTION WORK IN
POWER TRANSFORMER
Answer / raghavendran.r
In percentage differential relays, the current from each
current transformer flows through a restraint coil. The
purpose of the restraint coil is to prevent undesired relay
operation due to current transformer errors. The operating
coil current | i1 - i2 | required for tripping is a
percentage of the average current through the restraint
coils.
i1-i2 >=k(i1+i2)/2= k*iavg
where k is the proportion of the operating coil current to
the restraint coil current. For example if k = 0.1, the
operating coil current must be more than 10% of the average
restraint coil current in order for the relay to operate.
| Is This Answer Correct ? | 4 Yes | 0 No |
diff. between tension mode & speed mode
what is the difference between Resin Cast CT and Oil cooled CT?
What if the difference beween internal and exrteranal LBB?
why rating in KVA and KVAR?
Why is the starting current high in dc motor?
1600 KVA ka transformer hi aghar lt side par 800A aur voltage 420 ho to HT side ki cable ki rating keya ho gi?
What is the effect on 3phase induction motor if current setting knob of DOL kept at minimum current?
Differentiate AC and Dc resistance
What is the concept of voltage & current its relation?
what is the relation between Sq mm of wire and its current carrying capacity?
why one pin of plug pin is longer than other two? In some mobile chargers one pin is made not conducting .Why?
how to calaculate the amps in transformer ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)