Answer / rajesh tewari
current in primary
=kva*1000/1.732*primary voltage
current in secondary
=kva*1000/1.732*secondary voltage
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / prakash
Kva/1.732*kv for primary current
Kva/1.732*Lv for secondary current
Is This Answer Correct ? | 0 Yes | 1 No |
What will happen if we give the 3 phase supply to the rotor of slipring induction motor?
What should be the DC voltage for Hi-pot test on 11kv switchgear
L&T ACB C-POWER OF 800A FAULS TRIPING AT THE TIME OF 110KW MOTOR STARTS WITH EARTH FAULT RELEASE
Please clarify, 1. Is it required to lay two runs of GI wire along with Armoured LT cable if it is laid between one big mains (63Amps TPN SDF) to small main (32A TPN SDF) with proper glanding termination? 2. If the armoured cable with proper glanding is laid from DB to CNC machine, is it required to run two runs of body earthing to the Machine from DB? 3.If the armoured cable with proper glanding is laid from Substation to Hangar, distance is approx. 100 mtrs, is it required to do earthing at shop area though the primary termination at substation is earthed through gland.
In IDMT RELAY the term minimum (M) indicates what?
what is the differnce between high impedance relay and low impedance relay
what is the meaning of osr in transformer.
1. Why transfomer reting in KVA and Motor in HP
11 Answers AirIndia, Jindal, Mind Tree,
sir,in our plant we r using SATEC PM172E power reading meeters in HT panel side it is monitoring the MB data smart viewer(sever).but last one week we did not get readings inthe server only available in meeter.tell me how communicate meter and server. and also what steps we take for checking.
What will be cross section area of copper conductor for carry 2000 amps & 2500 amps....sq.mm.?/
HOW can i REuse the fused MLL LAMPS & GLS LAMPS at our factory
how much current take 16sq mm Cable