How does frequency affect KVA rating of a transformer?
If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz
frequency then how will its KVA rating change?
a-increase
b-decrease
c-remains same
Also explain why do u think like that.
Answers were Sorted based on User's Feedback
Answer / shaikh
Frequency is directly proportional to induced voltage of transformer (v=4.44NFphi). if you decrease frequency KVA will decrease and vice versa, because for the same rated voltage flux is also decreased and flux area of t/f decreases.
Is This Answer Correct ? | 47 Yes | 13 No |
Answer / k r vishnu narayanan
E/f = 4.44*N*phi(max)
E: induced emf
f: frequency
N: number of turns
phi: max flux in the core
When frequency is reduced keeping E constant(at E(max)), flux(phi(max)) has to increase (from eq:)to saturation and harmonics will come into effect. So, there has to be a maximum allowable voltage at a particular frequency and the current too is limited by the saturation effects implying that both V and I has to be limited at a particular frequency (maximum current is always limited by number of turns). Thus their product(kVA) has to be directly proportional to frequency and the answer to this question is b(decrease).
God bless...
Is This Answer Correct ? | 12 Yes | 1 No |
The transformer EMF equation shows that the EMF induced in the secondary or the primary side of a transformer is directly proportional to the product of the flux (Φm) through the transformer core and the frequency. This leads to the flux is proportional to E/f.
For example, the kVA rating of the 500v to 250v 60 Hz transformer will be smaller when used in Europe with a frequency of 50Hz. 500/60 = E/50, E is smaller than 500v on primary side. 250/60 = E/50, E is smaller than 250v on secondary side.
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / ashok kumar hudda
hey guys its simple yr
we say that transformers main aim is to maintain constant flux
so if we reduce the frequency for given size of transformer then we have to reduce the voltage to maintain constant flux so due to reduction in voltage KVA also decrease so we can say that KVA is directly proportional to frequency
Is This Answer Correct ? | 7 Yes | 0 No |
Answer / rajendra kumar
If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz
frequency then how will its KVA rating change?
expl-
kva rating depends upon V*I.
flux is same for both coil,
V1=4.44.N.f.phi
phi=k.V1/f=k.400/60=6.6
phi2/phi1=v1*f2/V1*f1=50/60=0.833
phi2=phi*0.833
V2 (sencondry side)=4.44 N2.f.phi2(at 50 hz)
=4.44.N2.f1*phi1
i.e no effect on voltage but flus has decreased means current will be decrease by factor 0.833.that is KVA=V*I2=V*I1*0.833 (decreases)
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / cameron hunter
The transformer EMF relation shows that the EMF induced in the secondary or the primary side of a transformer is directly proportional to the product of the flux (Φm) and the frequency. This also means that the flux is proportional to EMF over frequency.
As an example, for the 500V to 250V transformer, the kVA rating under 60Hz transformer will be smaller than 50Hz. 500/60 = V/50. V has to be smaller to keep consistency.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / nikhil singh
Transformers are rated in kva and not in KW for taking into
account the core and copper losses which are dependent on
voltage and current respectively without involving power
factor.Now the copper loss is independent of frequency but
the core loss comprising of hysterisis and eddy current
loss is proportional to frequency.So as frequency decreases
core loss decreases and KVA rating decreases.
Is This Answer Correct ? | 15 Yes | 16 No |
Answer / guest
remains same since kva rating depends on iron loss and
copper loss which means it depends on voltage and current.
Is This Answer Correct ? | 9 Yes | 44 No |
Can Dy11 and Dy1 vector group transformers be paralleled?
What is the difference between isolators and electrical circuit breakers?
which one is dangerous AC Power r DC Power for Electrical Shock ?
Do I need a special Transformer to put 240 VAC 3 phase into it and and get 480 VAC 3 phase out of it to run a machine? Or, do I just use an ordinary step down transformer and step up the voltage? Thanks
what type of oil is used in transformers? a)conduting b) insulating
25 Answers ABB, LGS,
we have 400kv/6.6kv transformer ,it has total 9 taps on HV side with normal tap on tap no 5.when we took the ratio test we observed that ratio was decreasing from tap 1 to tap 5 and was found increasing from tap 5 to tap 9.What is the reason?if anyone have related document then please send me on the email id ankushbahale@gmail.com......plz plz
What is CVT and what is relation with wave trap?
n1 =1000 n2 =?;v1 =200:v2 =400
Explain the function of VFD
What is sequence network? Discuss all three types of sequence network.
Why efficiency of generator is higher than motor at a particular load?
What is a liquid resistance starter?where it is used??