How does frequency affect KVA rating of a transformer?
If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz
frequency then how will its KVA rating change?
a-increase
b-decrease
c-remains same
Also explain why do u think like that.
Answers were Sorted based on User's Feedback
Answer / shaikh
Frequency is directly proportional to induced voltage of transformer (v=4.44NFphi). if you decrease frequency KVA will decrease and vice versa, because for the same rated voltage flux is also decreased and flux area of t/f decreases.
| Is This Answer Correct ? | 47 Yes | 13 No |
Answer / k r vishnu narayanan
E/f = 4.44*N*phi(max)
E: induced emf
f: frequency
N: number of turns
phi: max flux in the core
When frequency is reduced keeping E constant(at E(max)), flux(phi(max)) has to increase (from eq:)to saturation and harmonics will come into effect. So, there has to be a maximum allowable voltage at a particular frequency and the current too is limited by the saturation effects implying that both V and I has to be limited at a particular frequency (maximum current is always limited by number of turns). Thus their product(kVA) has to be directly proportional to frequency and the answer to this question is b(decrease).
God bless...
| Is This Answer Correct ? | 12 Yes | 1 No |
The transformer EMF equation shows that the EMF induced in the secondary or the primary side of a transformer is directly proportional to the product of the flux (Φm) through the transformer core and the frequency. This leads to the flux is proportional to E/f.
For example, the kVA rating of the 500v to 250v 60 Hz transformer will be smaller when used in Europe with a frequency of 50Hz. 500/60 = E/50, E is smaller than 500v on primary side. 250/60 = E/50, E is smaller than 250v on secondary side.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / ashok kumar hudda
hey guys its simple yr
we say that transformers main aim is to maintain constant flux
so if we reduce the frequency for given size of transformer then we have to reduce the voltage to maintain constant flux so due to reduction in voltage KVA also decrease so we can say that KVA is directly proportional to frequency
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / rajendra kumar
If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz
frequency then how will its KVA rating change?
expl-
kva rating depends upon V*I.
flux is same for both coil,
V1=4.44.N.f.phi
phi=k.V1/f=k.400/60=6.6
phi2/phi1=v1*f2/V1*f1=50/60=0.833
phi2=phi*0.833
V2 (sencondry side)=4.44 N2.f.phi2(at 50 hz)
=4.44.N2.f1*phi1
i.e no effect on voltage but flus has decreased means current will be decrease by factor 0.833.that is KVA=V*I2=V*I1*0.833 (decreases)
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / cameron hunter
The transformer EMF relation shows that the EMF induced in the secondary or the primary side of a transformer is directly proportional to the product of the flux (Φm) and the frequency. This also means that the flux is proportional to EMF over frequency.
As an example, for the 500V to 250V transformer, the kVA rating under 60Hz transformer will be smaller than 50Hz. 500/60 = V/50. V has to be smaller to keep consistency.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / nikhil singh
Transformers are rated in kva and not in KW for taking into
account the core and copper losses which are dependent on
voltage and current respectively without involving power
factor.Now the copper loss is independent of frequency but
the core loss comprising of hysterisis and eddy current
loss is proportional to frequency.So as frequency decreases
core loss decreases and KVA rating decreases.
| Is This Answer Correct ? | 15 Yes | 16 No |
Answer / guest
remains same since kva rating depends on iron loss and
copper loss which means it depends on voltage and current.
| Is This Answer Correct ? | 9 Yes | 44 No |
What is the rotor frequency of 10 Hp 1440 RPM 50HZ 415V ?
What is ESP how its work &what is corona ? con insulater&drive insulater where it is used ? Any body says that pls
3 Answers Travancore Titanium Products Ltd TTPL,
pls tell about gas insulated substation?which gas is used for that substation?above which rating we are used this substation?how we take maintenance in that substation?it means substation fully shutdown or live condition?if live condition means how?pls clear this things
what is the principle of generator, motor, and transformer and explain the definiton of flemings left hand rule , right hand rule and ohms law
what are the disadvantages of low power factor
HOW DOES THE ELECTRONIC ENERGY METER WORKS?
Why C.T secondary s2 done earthing?
how we are desining 63.5 ohm resistor for NGR of alternator?
what is recommended breakdown voltage of transformer oil?
What is done to avoid interference of high frequency transmission lines with communication lines??
WHY KVAR IMPORTANT WHEN ANY PLANT IS RUNNING ON IT'S OWN POWER PLANT?
In Power cable specification what is U0/U and Um.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)