How does frequency affect KVA rating of a transformer?
If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz
frequency then how will its KVA rating change?
a-increase
b-decrease
c-remains same
Also explain why do u think like that.
Answers were Sorted based on User's Feedback
Answer / shaikh
Frequency is directly proportional to induced voltage of transformer (v=4.44NFphi). if you decrease frequency KVA will decrease and vice versa, because for the same rated voltage flux is also decreased and flux area of t/f decreases.
| Is This Answer Correct ? | 47 Yes | 13 No |
Answer / k r vishnu narayanan
E/f = 4.44*N*phi(max)
E: induced emf
f: frequency
N: number of turns
phi: max flux in the core
When frequency is reduced keeping E constant(at E(max)), flux(phi(max)) has to increase (from eq:)to saturation and harmonics will come into effect. So, there has to be a maximum allowable voltage at a particular frequency and the current too is limited by the saturation effects implying that both V and I has to be limited at a particular frequency (maximum current is always limited by number of turns). Thus their product(kVA) has to be directly proportional to frequency and the answer to this question is b(decrease).
God bless...
| Is This Answer Correct ? | 12 Yes | 1 No |
The transformer EMF equation shows that the EMF induced in the secondary or the primary side of a transformer is directly proportional to the product of the flux (Φm) through the transformer core and the frequency. This leads to the flux is proportional to E/f.
For example, the kVA rating of the 500v to 250v 60 Hz transformer will be smaller when used in Europe with a frequency of 50Hz. 500/60 = E/50, E is smaller than 500v on primary side. 250/60 = E/50, E is smaller than 250v on secondary side.
| Is This Answer Correct ? | 10 Yes | 2 No |
Answer / ashok kumar hudda
hey guys its simple yr
we say that transformers main aim is to maintain constant flux
so if we reduce the frequency for given size of transformer then we have to reduce the voltage to maintain constant flux so due to reduction in voltage KVA also decrease so we can say that KVA is directly proportional to frequency
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / rajendra kumar
If a 500 kva, 400 v, 60 hz t/f is to be operated on 50 hz
frequency then how will its KVA rating change?
expl-
kva rating depends upon V*I.
flux is same for both coil,
V1=4.44.N.f.phi
phi=k.V1/f=k.400/60=6.6
phi2/phi1=v1*f2/V1*f1=50/60=0.833
phi2=phi*0.833
V2 (sencondry side)=4.44 N2.f.phi2(at 50 hz)
=4.44.N2.f1*phi1
i.e no effect on voltage but flus has decreased means current will be decrease by factor 0.833.that is KVA=V*I2=V*I1*0.833 (decreases)
| Is This Answer Correct ? | 7 Yes | 1 No |
Answer / cameron hunter
The transformer EMF relation shows that the EMF induced in the secondary or the primary side of a transformer is directly proportional to the product of the flux (Φm) and the frequency. This also means that the flux is proportional to EMF over frequency.
As an example, for the 500V to 250V transformer, the kVA rating under 60Hz transformer will be smaller than 50Hz. 500/60 = V/50. V has to be smaller to keep consistency.
| Is This Answer Correct ? | 6 Yes | 0 No |
Answer / nikhil singh
Transformers are rated in kva and not in KW for taking into
account the core and copper losses which are dependent on
voltage and current respectively without involving power
factor.Now the copper loss is independent of frequency but
the core loss comprising of hysterisis and eddy current
loss is proportional to frequency.So as frequency decreases
core loss decreases and KVA rating decreases.
| Is This Answer Correct ? | 15 Yes | 16 No |
Answer / guest
remains same since kva rating depends on iron loss and
copper loss which means it depends on voltage and current.
| Is This Answer Correct ? | 9 Yes | 44 No |
what is load shedding
Relay setting for earth fault of reciprocating and centrifugal compressor motor feeder.Setting will be different or same?
We have drive feeding an output contactor for a 5000 hp motor @ 5kV application. The motor FLA is 629amps x 1.25% service factor = 786.25 amps The cable that we current have in place between the drive and the output contactor is 350kcmil- MV-105 (parallel cables). Per the NEC table 310.60 (C) (69). This show the cable ampacity is at 615 amps per cable for a rating of 1230 amps. We have derated the cable for the cable tray and the multiple cables application and our calculations show that after the correction factor factor we are at 922amps. 1230 amps x .75% correction factor factor = 922.5 amps. The customer is driving us to then use another safety factor of .25% off of the already derated cable. Can you please provide a longhand calculation for your solution on this application?
In PFI plant one stage capacitor connection is directly connected(with out megnetic contact controll). but why?
what is the meaning of 1250 KVA Trasformer
How to calculate busbar size & what is the procedure we make for determine that?
35 Answers Auko Tex, Integra, PowerTech, Shadhin Group,
how to fit 3 HP crompton gear motor with conveyor with the use of staring delta starter or ordinary starter?
what perpose of use CT ratio in gt,st,uat
Why we transmit the power at the voltage in the multiple of 11 or 1.1 like 11kv, 22kv, 66kv, 132kv...... some one told me that it is due to fomr factor 1.1 of sine wave. its fine but while transforming we can choose any voltage, so why only multiple of 1.1 there also.......? plz tell me.
if two heater of rating 1KW,200v are connected in series 100v supply what will be the power taken
What is the operating range(tolerance) of voltage and frequency of grid supply in india?
Does the motor power displayed on the Motor name plate is the mechnical power motor delivers or it is consumed power from the system?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)