WHY TRANSFORMER RATING IS MENTIONED IN KVA RATHER THAN KW
Answers were Sorted based on User's Feedback
Answer / guest
because transformer output power depends on total losses i.e
iron and copper loss
Is This Answer Correct ? | 9 Yes | 4 No |
Answer / tank
The transformer is an apparatus which receives the power in
VA,KVA or MVA rating depending upon the capacity of the
transformer and it transforms/supplies the power under same
rating to a particular load when it is connected to a
transformer.In this process the power factor of the
connected load decides the KW rating(KVA X P.F = KW).Hence
transformer rating is never given in KW but always in VA,
KVA or MVA at manufacturing stage as there is uncertainity
of the type of the load and power factor to be connected
with the transformer.
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / parthi
The copper loss of
transformer is depent
on the current and iron
loss is depent on the
voltage. The losses
are does not depent
on the frequency so
the transformer
ratings are in Kva not
in kw.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sunil
Transformer is electrical equipment and hence delivers in
rated KVA. kW is what we use after pf, losses etc.
Is This Answer Correct ? | 0 Yes | 1 No |
Answer / baljeet singh
The transformer is a power source device ,It transformer electricity from one medium to another medium.Due to this power factor not take on part.So transformer rating alwas in kva not in kw
Is This Answer Correct ? | 1 Yes | 8 No |
Slip at maximum torque depends on A rotor resistance and reactance B stator reactance C load current D stator resistance
What are the details of ratings of different types of ACSR conductors?
why put integration for capacitorand differation for inductance
What is the difference between Class PX & Class X CT's
megger generates D.C. voltage while earth tester generates A.C.voltage is it true? I know for megger it is D.C generator but what about earth tester?
3ph motor running with unequal kw and different pf what are the reasons
what is the difference between MCCB and SFU in terms of their application?
2 Answers Secure Meters, Tata Teleservices,
why incomer bay is required before transformer bay if there are more than 1 nos. of transformer bay.
What is the effect of electric motor stuck in star configuration,
What is ignition module of a CAT Gas Genset G-3508 Engine, Alternator SR4B Series. HOw its checked for correct functioning.Is it repiarable or replacable?
I am abt to give IOCL intrv.Plz sir guide me for IOCL intrvw (Electrical).Which subject to be consider. questions are generally asked from which subject.Plz help me out.
As per BIS, Earth pit resistence value?