Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate transformer capacity requirement for a
project site?

Answers were Sorted based on User's Feedback



How to calculate transformer capacity requirement for a project site?..

Answer / mahesh sali

THE CAPACITY OF TRANSFORMER USED FOR SITE APPLICATION SHALL
BE CALCULATED BY FOLLOWING CONSIDERATION;

CAL.TOTAL CONNECTED LOAD
BASE ON KW & ASSUMATION OF 0.8 P.F.
CAL. THE KVA/ MVA RATING OF X'MER I.E. KW/0.8
AFTER GETTING KVA/MVA ADD THE 20% IN CAL.KAV/MVA

I.E. KVA/MVA + 0.2*KVA/MVA

20% EXTRA AS PER IEEE RULE

AS PER IEEE NORM ,UR TRANSFORMER SHOULD BE LOADED AT 80% OF
UR FULL CAPACITY OF UR TRANSFOMER.

I HOPE ABOVE INF. IS SUFFICIENT.

THANKING U

Is This Answer Correct ?    26 Yes 1 No

How to calculate transformer capacity requirement for a project site?..

Answer / vathnak kong

Example
We have Power load 2300KVA
So
Transformer Capacity=2300×1.4
1.4 is Power rate

Is This Answer Correct ?    6 Yes 1 No

How to calculate transformer capacity requirement for a project site?..

Answer / sivaguru

Hi Mr.Mahesh

Can you please forward the IEEE rule showing the
transformer loading of 80% of full load as you
discussed....Kindly forward it to my email id
sivaguru_691984@yahoo.co.in...

Even we haven't took tr. loading factor for all our
projects and we will be really educated by pupil like you
for the need of consideration of transformer loading
factor...

Is This Answer Correct ?    2 Yes 0 No

How to calculate transformer capacity requirement for a project site?..

Answer / thanigai1984

Now a days...
we calculated the connected load ...in KW and 40%
assumption load will be added

Transformer cap=60% load connected +40%

Is This Answer Correct ?    4 Yes 2 No

How to calculate transformer capacity requirement for a project site?..

Answer / sunil biswal

Calculate all connected loads(KW) Assume Fans as 65Watt,15A sockets as 1000Watt, 5A Sockets at 1ooWatt, TV at 120 Watt Computer at 120Watt, Printer/Scanner/Copier at 1000Watt, A/C 1.5 Ton at 1.5KW
Apply diversity Factor since all loads will not be working at the same time always
Divide the single phase loads into 3 parts. (KW)
Then add three phase loads and i/3rd single phase loads(KW)
add 20% extra to this calculated gross KW
Divide by power factor 0.8 to get KVA Rating of transformer.
At this point you may add another 20% to the rating as a factor of safety and reliability since most machine work comfortably at 75 to 80% loading
Now decide the actual rating of transformer in proper slab as the standard ratings transformer are available in are 10KVA,16KVA,25KVA,63KVA,100 KVA, 125KVA, 160KVA, 200KVA, 250KVA, 500KVA in 11KV range.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

mostly the questions were from machines... d.c. machines, transformer, synchronous and induction all theory paper........ few from power system... but the level of paper was easy.....

0 Answers   IFFCO,


why we connect the capacitor bank in star , not in delta in any system

2 Answers  


why high voltage is reqiured or L.T. panels? what type of tests should be taken for electrical panels?

2 Answers  


why to need a electrical earthing?

2 Answers  


Whai isPCC and MCC Difference?

1 Answers   Pretech Plast,


help!!!! i bought a new house 2 yrs ago,ive just had 2 new lights fitted,when i boil the kettle,maybe 2 times in succession the safety light switch trips out,it dosnt do it straight away but it seems to do it when the kettle boils!!!!! sounds very odd to me

2 Answers  


How many no of flip-flops are required to get 16 bit counter

10 Answers   HAL,


Which device of PlC does share load between DG sets when DG are running in perallel?

0 Answers  


What are the main problems in distribution? I have to do an assignment so which problem should I choose? Like power factor problem etc.

4 Answers  


how to calculate the earth mat design in 132 kv substation yard ????

0 Answers   Divis Laboratories, KSEB, SWPL,


Any formula to calculate neutral current in 3 phase 4 wire system

1 Answers  


What is the power plant or power station?

1 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4453)
  • Electrical Engineering Interview Questions Electrical Engineering (16638)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)