Golgappa.net | Golgappa.org | BagIndia.net | BodyIndia.Com | CabIndia.net | CarsBikes.net | CarsBikes.org | CashIndia.net | ConsumerIndia.net | CookingIndia.net | DataIndia.net | DealIndia.net | EmailIndia.net | FirstTablet.com | FirstTourist.com | ForsaleIndia.net | IndiaBody.Com | IndiaCab.net | IndiaCash.net | IndiaModel.net | KidForum.net | OfficeIndia.net | PaysIndia.com | RestaurantIndia.net | RestaurantsIndia.net | SaleForum.net | SellForum.net | SoldIndia.com | StarIndia.net | TomatoCab.com | TomatoCabs.com | TownIndia.com
Interested to Buy Any Domain ? << Click Here >> for more details...


How to calculate transformer capacity requirement for a
project site?

Answers were Sorted based on User's Feedback



How to calculate transformer capacity requirement for a project site?..

Answer / mahesh sali

THE CAPACITY OF TRANSFORMER USED FOR SITE APPLICATION SHALL
BE CALCULATED BY FOLLOWING CONSIDERATION;

CAL.TOTAL CONNECTED LOAD
BASE ON KW & ASSUMATION OF 0.8 P.F.
CAL. THE KVA/ MVA RATING OF X'MER I.E. KW/0.8
AFTER GETTING KVA/MVA ADD THE 20% IN CAL.KAV/MVA

I.E. KVA/MVA + 0.2*KVA/MVA

20% EXTRA AS PER IEEE RULE

AS PER IEEE NORM ,UR TRANSFORMER SHOULD BE LOADED AT 80% OF
UR FULL CAPACITY OF UR TRANSFOMER.

I HOPE ABOVE INF. IS SUFFICIENT.

THANKING U

Is This Answer Correct ?    26 Yes 1 No

How to calculate transformer capacity requirement for a project site?..

Answer / vathnak kong

Example
We have Power load 2300KVA
So
Transformer Capacity=2300×1.4
1.4 is Power rate

Is This Answer Correct ?    6 Yes 1 No

How to calculate transformer capacity requirement for a project site?..

Answer / sivaguru

Hi Mr.Mahesh

Can you please forward the IEEE rule showing the
transformer loading of 80% of full load as you
discussed....Kindly forward it to my email id
sivaguru_691984@yahoo.co.in...

Even we haven't took tr. loading factor for all our
projects and we will be really educated by pupil like you
for the need of consideration of transformer loading
factor...

Is This Answer Correct ?    2 Yes 0 No

How to calculate transformer capacity requirement for a project site?..

Answer / thanigai1984

Now a days...
we calculated the connected load ...in KW and 40%
assumption load will be added

Transformer cap=60% load connected +40%

Is This Answer Correct ?    4 Yes 2 No

How to calculate transformer capacity requirement for a project site?..

Answer / sunil biswal

Calculate all connected loads(KW) Assume Fans as 65Watt,15A sockets as 1000Watt, 5A Sockets at 1ooWatt, TV at 120 Watt Computer at 120Watt, Printer/Scanner/Copier at 1000Watt, A/C 1.5 Ton at 1.5KW
Apply diversity Factor since all loads will not be working at the same time always
Divide the single phase loads into 3 parts. (KW)
Then add three phase loads and i/3rd single phase loads(KW)
add 20% extra to this calculated gross KW
Divide by power factor 0.8 to get KVA Rating of transformer.
At this point you may add another 20% to the rating as a factor of safety and reliability since most machine work comfortably at 75 to 80% loading
Now decide the actual rating of transformer in proper slab as the standard ratings transformer are available in are 10KVA,16KVA,25KVA,63KVA,100 KVA, 125KVA, 160KVA, 200KVA, 250KVA, 500KVA in 11KV range.

Is This Answer Correct ?    1 Yes 0 No

Post New Answer

More Electrical Engineering Interview Questions

How to calculate meter constant @ HT yard

5 Answers   Juniper Networks,


In three phase, phase to phase voltage is 440 Volts, but the three phase motors are designed for 415 Volt, 50 hz, why

1 Answers   Shree Ram, Shriram, Sri Ram,


what is the effect of connecting three phase supply lines to three phase auto transformer output terminals through a fuse of 10Amp and a circuit breaker (MCB). Is this connection permanently destroy the transformer?

1 Answers  


Why transformer neutral earthing? What is advantages?

3 Answers  


how to calculate circuit breaker capacity

6 Answers   Siemens,


What is acsr cable and where we use it?

0 Answers  


should %impedance be high or low in a power transformer? if so why?

0 Answers  


In Energy meter How many rotation Equal to one unit.

3 Answers  


i want to estabilish an loss energy storage system,such that it can store electricity lost during the transmission of electricity in conductor,so that this system stores energy lost during transmission and supply it to street lights during night

2 Answers  


why the amount of voltage generated at power generating stations is 11 KV only....?

3 Answers  


what r the tests on the 3 phase transformers can any one explain how to test using megger on transformers thx

2 Answers  


Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise,give with best examples.... please help me in this regards....

1 Answers   Modi Builders,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5086)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4456)
  • Electrical Engineering Interview Questions Electrical Engineering (16639)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)