How can we do megger test of cable??
Answers were Sorted based on User's Feedback
Answer / sridhar nayak
by the help of tester the insulation of the cable canbe
measured. the simple technique is just raotate the handle
of the megger and place the test prod one on conductor and
other on the insulation it should not show less then 2mohms.
Is This Answer Correct ? | 16 Yes | 2 No |
Answer / savarkarshriram
If cable is rated for 1.1KV the megger test( Insulation
resistance test) is done with use of 500V or 1000V.
The test probes are connected across each phase , neutral
and ground terminal so that it covers all combinations.
If it is HT cable then 2000V IR tester is used. with the
same method as explained above.
Thumb rule for minimum value is 1M ohm per KV of rated
volatge of equipment
( Mind you megger is name of company and not name of test
so engineers should use term insulation resistance rather
than megger)
Is This Answer Correct ? | 3 Yes | 0 No |
How to design inductive load for 3 phase 440v and maximum 5 amps for star or delta? Can we use a 15kW, 1450rpm motor for 15kW, 960rpm apllication?If yes.how......n.if thesame motor used what`s it`s sideeefect.
as ac supply is given 2 the transformer why it doesnot depends upon powerfactor????
How to select the rating of a CT used for REF protection. The rating can be of equal rating of Phase current or neutral current rating
can we replace d.c.motor by 3 phase induction motor for a particular application
What is transformer saturation?
What is accuracy of a measurement?
i am swathi, b.tech 4th year. In smps(switched mode power supply)we are using diodes,mosfets,igbts for controling of current. And my question is why we did not use thyristors(scr)? it is also act as a switch,then what is the drawback of scr as compared to above transisters> if we use the scr,then what is happening ? plz give reply as soon as possible bcoz i am doing project on smps. plz frnds i want ans for that. if anybody know the ans plz send to my e-mail id /swathi.tadakapally@gmail.com/
What is harmonics in AC waves. How it is generated? How it will effect the system network? how can eliminate it?
defination of controlled shunt reactor
What is In (current rating) shown on the MCCB? Is this full load which can withstand by the circuit breaker
how to calculate the battery AH
hi can you give any body fault level calculation, generator fault level calculation,transformer fault level calculation for system fault level with equation? i have 3.3kv generation voltage three gas gen sets, one is 1.9MW,2nd is 2.5MW,& 3rd is 3.8MW & i have 11 kv generation voltage one gas gen sets is 3.8MW, we are step up to 22kv by transformer
3 Answers Hindalco, Piramal Healthcare,