What are the advantages and disadvantes of delta and star
connections in transformers and alternators?
Answers were Sorted based on User's Feedback
Answer / vasudeva rao
1)in star there is a possible of neutral (i.e return path)
but in delta thereis no return path
2) in star phase current and line currents are same (Iph =
IL) but in delta (vph = vL).
| Is This Answer Correct ? | 17 Yes | 2 No |
Answer / karthick
in star IL=IPH .......... in delta VL=VPH
accoding to kirchofs law meeting towards point and away
from point is equal to zero
so in star neutral is done
no neutral in delta connection
| Is This Answer Correct ? | 10 Yes | 3 No |
Answer / jwalith
in case of alternators
generally star connection is preffered because it has a flushing out point for odd harmonics but whereas delta connection lets it circulate inside itself..
| Is This Answer Correct ? | 6 Yes | 3 No |
we have 3.5MVA-11/6KV transformer. how can we calculate earth fault current and NGR calculation?
KVA transformer of different frequencies of 50hz,100hz,500hz&1000hz. which one of these transformer has big size? Give reason
What is meant by earthhing of a magnetic flow meter and when to use empty pipe detection?
What is a DC series motor?
What is working principal of V.C.B., O.C.B., A.C.B & Over load relay?
1)What are the proccedure of initial charge of 100AH lead Acid battery bank 2)whether discharge test is reqd ? if it is rqd why, how 3)what are the discharge critieria (volt/cell or sp.gravity/cell
HOW TO CALCULATE GROUND FAULT CURRENT IN 430V 4000AMP AIR CIRCUIT BREAKER?
Define Current Transformer? Working & TYpe's Of C.T.
How open delta used for protection?
A resistance, inductance & capacitance are connected in series between points A & B.The voltage drops across the resistance,inductance&capacitance are found to be 40V,70V&100V respectively. What is the total voltage between between points A&B (Vab)? a)210V b)70V c)50V d)230V
What is the difference between harmored cabled and unharmored cables
my motor rating is 800HP, 128Amps, 3.3kV. What is capaitor bank i can use for PF improvement to 0.990?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)