I have three phase 400 KW,390 A MOTOR.For this motor which type
of Cable is required....specifically rubber cable required. Can
anyone help me..
Answers were Sorted based on User's Feedback
You mentioned the current capacity of motor is 390A, If
distance is too closer to the breaker,then you might be go
for copper cable, it will have lesser cross section and
high current carrying capacity. If the distance is more
better to go for the Aluminium cable so that cost of the
cable will reduce from the copper cable.
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / abhishek
dude you have not mentioned the rated vol of the motor
Is This Answer Correct ? | 2 Yes | 0 No |
Answer / padmakumar
Cable size selection is dippending on several factors like
current,distance,cable routing, nature of load,duration of
running of equipment etc.Normally 400KW LT motors nobody
prefers to run due to high current handling.HT motor is
preferable.In case of LT, you can go ahead with 400sqmm two
runs of Alumonium cable with stardelta starter.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / ramjilal
first your question is wrong 400 KW motor current more than
390 amps. second you not mention type of starter.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / bhupat chaudhari - adani
you should be going with 400 sq al xlpe cable for long
distance and with star-delta..
Is This Answer Correct ? | 0 Yes | 0 No |
WHAT IS ND RELAY AND HOW DOES IT WORK?
what is the prinsiple of dc motor and construction and working ,application of dc motor.
can transformer of different kvas be paralled
11 kV line deraction check by an Engineer.
why impudance relay used for medium transmission power system? why not others?
what will happen if frequency is below 50 hz?
What is icu and ics in Acb and how many time icu or ics passes from breaker?
if voltage in transmission line more than current will be more or less,if less what about the Ohm's law
How to check the LM324 Ic
how to select fuse rating for a 3-phase motor ???
what are the factors to be considered while design the breaker either HT or LT??
Transmission through a short line depends on