how calculate cable size in squre mm, when the load is
given by in kw? do u have current rating chart of elctrical
cables?
Answers were Sorted based on User's Feedback
With knowing the kW rating and voltage, the current can be
calculated as I=P/(sr(3)*V*pf). The pf can be assumed to be
as 0.8. After knowing the current, choose the 10% higher
current carrying capacity cable for the safety purpose.
current rating for differnt cables are different for same
size.Copper has higher current carrying capacity.
Is This Answer Correct ? | 10 Yes | 2 No |
Answer / moh. baheer
We can so easy calculate the current and choose the cable
size form chart if we have the quantities of Voltage (Volt)
and total power (KW) please find from this formula the
current rate according to the load (kW).
P = U*I*cosФ
I = P/U =?
Then we can choose the cable size from chart according to
current.
Regards
Is This Answer Correct ? | 4 Yes | 1 No |
Answer / shahidul islam (srabon)
When the power is known in kW then the formula for knowing
the current in A is I=(P/(sr(3)*V(phase)). Now we the
current. After finding the current we know that the current
density of copper is 2.5. Finally to calculate the cable
isze we apply the given formula in practice.
I=A*2.5
so, A=I/2.5 (in square mm)
Where A=Area of conductor or here cooper is used
A=w*l
w=width
L=length of the conductor
Hope the answer of the question
Is This Answer Correct ? | 2 Yes | 2 No |
Answer / abdul rahman
While all loads are given in KW,only current matters while calculating cable sizing assuming voltage remains constant neglecting minor fluctuations.
From power equation once u find the load current you decide the cable sizing.As a thumb rule 1sq mm of Cu carries 2.4A whereas Al carries 1.4A.
For example a 100kw load requires nearly 180A current.The cable sizing would be 4core X 95 sqmm Cu plus 1core 50 sqmm ECC.
Different manufacturers have their standard sizes hence the value main differ slightly but the thumb rules will help u.
Is This Answer Correct ? | 0 Yes | 0 No |
What is the difference between Earthing & grounding
List out the types and name of the motor under their application?
I have a 25 KVar capacitor bank at my facility.How to check the capacitor bank ??
why there is no current in the rotor body althrough the flux linking with it also get changes. why current only flows in windinds not in rotor
what is tandem isolator ??????????
HOW TO CALCULATE THE CABLE SIZE FOR POWER CABLE, CONTROL CABLE AND INSTRUMENT CABLE
what is power factor
how to check the continuity of a cable with a megger
How much depth n width required for laying of 1X70 Sqmm Cable in Desert???
0 Answers Alka Electromech, Aramco,
what will happen if field winding of Synchronous generators given ac supply
is there any device that works properly accept relay, it may be fuse but if i want fuse of 33kv 300 amp it is avaliable, pls give me details
what is basic difference betmeen normal & flame proof motor??