Why is the generator rating always in kVA and motor rating
in kW?
Answers were Sorted based on User's Feedback
Answer / ranjeet
transformers are rated in kva because copper loss is due to current and iron loss is due to voltage so it is expressed in va and power factor is not know
| Is This Answer Correct ? | 11 Yes | 3 No |
Answer / jayesh pillai
the load on generator or transformer is not known so its
power factor is also unknown
moreover active losses occuring in transformer is very low
due to these reasons generator or transformer are having
rating in kva and motor is in kw
| Is This Answer Correct ? | 4 Yes | 1 No |
Answer / k.sri405
generator is a power source so the load of generator is not
known it may either inductive or resistive or capacitive.
and power factor depends on load so it is rated in kva. but
motor itself is a load so it is rated in kw.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / vamsi
trf having two losses 1.copper losses depends on current and iron losses depends on voltage.so trf having unknow power factor.it depends on nature of the load i.e restive,inductive and capacitive load bt motor having fixed power factor and its doesnt depends on load.
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / sumit kumar
In the case of t/f eddy current loss and hysterisis loss due to current so, the rating of t/f is in kva but in case of motor loss is i^2*r so,rating in kw.
| Is This Answer Correct ? | 1 Yes | 5 No |
Answer / qwde
Aternator's & Xmer's power factor depend on threir loads.
So that u can not calculate KW rating at the time of
manufacturing.
| Is This Answer Correct ? | 0 Yes | 5 No |
Answer / shareef
The simple answers are
1- Motor & Loads devices specify by KW
2- Generator, transformer, OHTL, UGC...ect (any devices
used to transfer, improve or generate the power is
specified by KVA)
| Is This Answer Correct ? | 1 Yes | 7 No |
What is the Surge suppresor? Why using in a UDB's and How it works?
why battery is connected in series?
We know that, in case if there is a faulty insulation,or sc, the current is bypassed to earth through the earth wire that has low resistance.Actually, what will happen to that current that flows through gnd?In that case,if we come in contact with that faulty appliance, wont that current flow through us as we form a closed path by standing in gnd?Is grounding a safety measure?
what happen if one of 3-phase line has a much higher load when we are using delta to star transformer? how we can over-come from that?
give me the details of anti pumping relay
why are transformers rated in KVA and not in KW
Can I use 1 phase power supply to run 3 phase motor? If yes, how?
What is the use of bundle conductors?
what is destructive and non-destructive testing of welding
defination of generator
Is it required to use Automatic transfer Switch in L&T panel board if we use AMF panel with DG set? How the single line diagram will be? Please forward the material to sreenu_207@yahoo.co.in
What is boucholz relay and the significance of it in to the trformer?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)