What is the acceptance value of leakage current in HI POT test
Answers were Sorted based on User's Feedback
Answer / c.hari balakrishnan
SWITCHGEAR : -
There is no specified value of leakage current,Normally it
depends on how much load is connected.Normally it is in
milliamps.For example : In 11kV SWGR we highpot with 20bays
(indoor SWGR)we can get around 20 to 30 mAmps...
Cable: -
for cables normally we can get around very low Milliamps...
| Is This Answer Correct ? | 8 Yes | 8 No |
Answer / tharindu eroshan henadawithara
3 mA for 11 kv for my sites,and really it is possible in 3c240 xlpe/pilc joints(new ,short distance).
3c240 pilc possible with 8mA max(length and old)
dry country with under ground system.
no rain at all..(no effects from water,but may from see)
| Is This Answer Correct ? | 1 Yes | 3 No |
Detailed working of a diesel generator set ?
1 Answers Airtel, Honda, Kirloskar,
is synchrnous pannel is need for two eqal rating transformers to run in parallel
What is the alternate solution for testing of polarity by using polarity tester while its milli ammeter does not works?
Why a single-phase induction motor not an inherently self-starting machine?
11 Answers ETC, Hindustan Shipyard,
Hi.. I am a BE GRaduate in E&E. I have 8.5 Experience in Tendering & Estimation field. I have done SAP SD course few years back. But due to some reason i failed to get job in that field and continued my own field. Now I am thinking of changing into SAP seriously. How should i go ahead???
I have carried out wiring for lighting in a shed in Industrial area which contains Metal halide lamps & have balanced in 3ph.Now when we put all the lines on in the daytime the current taken at 3phases at MCB comes to be equal i.e.28,29,28Amps respectively but in the night time i.e between 7p.m.to 11p.m. at the same MCb the current is 52,59,62Amp, though I have fit 63A MCB it is tripping in the above period.What may be the reason.? Note: This industry is located in industrial area where majority of steel ingot manufacturing plants are there. Whether this may be due to harmonic? what should I do to overcome above problem.pl suggest urgently.
Before i went to bed my master bathroom lights were working fine. At 2 am, when I went to use the lights, none of them were working. The outlets throughout the bathroom work, but the lights and fan above the toilet don't. I have two panels of switches. The one panel has four switches. One of the switches turns on the hall light, and that works. The other three are to other lights, and they don't. The other panel has three switches. One of those is to the fan, and the other is to a light above the toilet. The other is a to light that is also on that other panel. I tried the breakers, and the one that turns off the outlets, marked for the bathrooom, turns on and off the outlets. None seemed to be tripped. I checked the lightbulbs, and they are fine. Please help
which have higher efficiency transformer or induction moter
where HT & LT capacitor uses ?
How to take of Transformer oil Break down voltage test?
11kv/433v delta/star distribution transformer primary side full load Ht current is 83.33A in , but input side VCB rating 800A.why?
In a poly phase circuit if clamp on meter shows same load on three phases and their sum on neutral then why we use three and a half core cable or maximum the same size of core as that of phase?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)