How voltage regulation is calculated for over head
transmission line? What do we mean by Conductor constant
while calculating voltage regulation? how it is differ for
for diffrent type of conductor say AAAC DOG & AAAC RACOON
conductor?
Answers were Sorted based on User's Feedback
Answer / vinaya
Calculation of voltage regulation is an important part of power system analysis.
ACSR, AAAC conductors of different sizes are available. Usage of a particular conductor depends on factors like voltage rating of the transmission line, power factor, total load, length of the line etc. For example following are the KW-KM values for 1% voltage drop at 60 deg C at P.F
1.00 - 41613; 0.9 - 25438; 0.8- 20966; 0.7- 17787 FOR acsr Coyote 26/2.54 + 7/1.91 conductor.
Generally the formula used for calculation of Regulation is
% regulation @ --- p.f = KW-KM X RC of conductor/P.F x D.F
| Is This Answer Correct ? | 14 Yes | 6 No |
Answer / shiva
The above ans is general for calculating the regulation in
T.L. Due to capacitance effect in overhead transmission line
(short, medium, long) the regulation forumula is vaired.
| Is This Answer Correct ? | 12 Yes | 8 No |
Answer / sks
Voltage Regulation is denoted in percentage.
Voltage regulation[%]= Vs-Vr*100
-----------
Vs
Vs = Voltage at Sending end.
Vr = Voltage at Recieving end.
different type of Conductor are useful as per current
carring capacity,resistance,length of
line,weatherproff,economics, market avilability, apearance
etc.
| Is This Answer Correct ? | 14 Yes | 11 No |
What happen if we apply square wave or traiangular waveform voltage to the transformer primary winding instead of sinusoidal wave?
in thermal overload relay class 10A indicate what
If you don’t have coal, salt and copper, then how would you earth your connection temporarily at a camp site.?
what is zero sequence curr ent ?
What are the applications of autotransformers?
what is the difference between relay and a contactor.
can we use optical fibre to electrical power transmission ?
FLP zone Types and Details
WHAT IS THE PARTIAL DISCHARGE TEST?
why transformer rating is given in kva?
what is the significant for using two types of voltage(line voltage & phase voltage)
Why 4 pole generator generates more power and 6 pole generates less power campare to 4 pole
2 Answers Julius Berger, Suzlon,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)