How voltage regulation is calculated for over head
transmission line? What do we mean by Conductor constant
while calculating voltage regulation? how it is differ for
for diffrent type of conductor say AAAC DOG & AAAC RACOON
conductor?
Answers were Sorted based on User's Feedback
Answer / vinaya
Calculation of voltage regulation is an important part of power system analysis.
ACSR, AAAC conductors of different sizes are available. Usage of a particular conductor depends on factors like voltage rating of the transmission line, power factor, total load, length of the line etc. For example following are the KW-KM values for 1% voltage drop at 60 deg C at P.F
1.00 - 41613; 0.9 - 25438; 0.8- 20966; 0.7- 17787 FOR acsr Coyote 26/2.54 + 7/1.91 conductor.
Generally the formula used for calculation of Regulation is
% regulation @ --- p.f = KW-KM X RC of conductor/P.F x D.F
Is This Answer Correct ? | 14 Yes | 6 No |
Answer / shiva
The above ans is general for calculating the regulation in
T.L. Due to capacitance effect in overhead transmission line
(short, medium, long) the regulation forumula is vaired.
Is This Answer Correct ? | 12 Yes | 8 No |
Answer / sks
Voltage Regulation is denoted in percentage.
Voltage regulation[%]= Vs-Vr*100
-----------
Vs
Vs = Voltage at Sending end.
Vr = Voltage at Recieving end.
different type of Conductor are useful as per current
carring capacity,resistance,length of
line,weatherproff,economics, market avilability, apearance
etc.
Is This Answer Correct ? | 14 Yes | 11 No |
what is surge impedance loading and it's significant in power system?
why is efficiency of transformer more than that of other rotating machines?
What is force on a conductor in a magnetic field ?
the site measured knee point voltage of protection class CTs should be greater than rated knee point voltage? what about meetering class CTs. Should it be below the rated knee point voltage?
How to calculate pitch, gauge of winding wire, and No. of turns for 30HP, 3 phase, 4 poles 50Hz, 380V induction motors
how is the testing of an REF relay? what are the test REF circuit having?
show the single line diagram of star delta starter with single phase preventer
How do ACB are maintenance, what are the problem occurred in ACB
Calculate torque developed by the 3-phase, 5 H.P., 4 pole induction motor runs at 1500 rpm A 23 N-m B 21 N-m C 10 N-m D 0 N-m
can we use the same fuse for both ac and dc?
what is V.L.F. testing of power cable? do you know the voltage ratings, like for what rating and size of cable what rating of V.L.F. testing is used?
what is the workimg of ct &pt?