What size cable is used for HT cable to the transformer of
630kVA, and the supply voltage is 11kV
Answers were Sorted based on User's Feedback
Answer / pradyumna chandra panda
k prakaschandra is correct. * 35 sqmm 3core aluminium conductor is sufficient because 630KVA transformer full load current is 31.5 amp and 35 sqmm al conductor can take 70 amp current.
Is This Answer Correct ? | 4 Yes | 2 No |
1.what is meaning of curve into a mcb. 2.what is basic reason changing of curve
Define what is the function of anti-pumping in circuit breaker?
What is the different between Earthing & grounding?
What the difference between ac and dc inductor an capacitor
How the size of transformer decreases if we increases the frequency?
To transmit the Power which must be present…? a) Reactance b) Resistance c) Capacitance d) none of above
wht do u mean by load in circuit.wht dp u mean by inductive load
Why iron core losses are constant at all loads in a transformer ?
what happend if the protection ct is by mistake put instead of measuring ct & vice versa?
Is it possible to run HT motor through LT VFD (LT VFD supply given to Transformer LT side and transformer HT side connected to motor)
what happen if generator exitation lost?
What is meant by a stray loss of a induction motor??? What is the equation to find it