What size cable is used for HT cable to the transformer of
630kVA, and the supply voltage is 11kV
Answers were Sorted based on User's Feedback
Answer / pradyumna chandra panda
k prakaschandra is correct. * 35 sqmm 3core aluminium conductor is sufficient because 630KVA transformer full load current is 31.5 amp and 35 sqmm al conductor can take 70 amp current.
| Is This Answer Correct ? | 5 Yes | 2 No |
I have a 5KVA UPS. Total load to be connected almost 3KW. Ordering a battery pack with capacity of 1920VAh. How long will the backup time be?
Pl. share your experience about industrial-electronics repair of machine tool.
What is instrumental error?
pls tell what are doing the three phase motor star and delta connetion with circuit diagram and control wiring .
What is the minimum insulation value required for a cable between phase to phase and phase to earth of 380 Vac 50Hz circuit, having load arround 800 amps.
we have 15 ampere variyac but we want 30 ampere variyac what we do
how calculate the electrical load for industry and office
What is the Power Plant.
What is the difference between power,voltage,current? and with example
how to check ac servo motor
What is Specific Gravity of the Electrolyte used in Lead Acid Battery????What is Unit????
whatis knee point ?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)