Answer / sam

Capillary level transmitters are the best for just about any
application but they are very expensive compare to a normal
DP Cell with tubing.
The problem with these capillary transmitter installations
are that a lot of installations and designs are done without
flushing rings and equalization tubing and valves. This then
have to be installed afterwords since they are needed during
calibration once you start working on vessels with a process
pressure of 10bar and up. Without these the calibration will
become more inaccurate the higher your vessel process
pressure is. Be aware we still have static alignment
problems even in this day and age of smart technology.
Unless you do a process zero before your calibration you are
going to pick up problems and the only way to do a process
zero is if these flushing rings and tubing is installed from
the HP to the LP tap off points.
Good Luck

Is This Answer Correct ?    1 Yes 0 No

Why do we need to install hook-up line differential pressure type level transmitter when the diffe..

Answer / kinst

I don't know the answer of the question. that's why i asked
this question.

Is This Answer Correct ?    0 Yes 5 No

Post New Answer

More Instrumentation Interview Questions

what master plc do?

2 Answers   ISRO, Yokogawa,


why bevelling is done in an orifice ?

4 Answers   ABB,


what is concept of field,control room area in transmitters?

1 Answers  


flow transmitter formula?

0 Answers   BEMCO, Siemens, Yokogawa,


principle of rtd

4 Answers  






What is passive connection of instrument in different types of IO module?

2 Answers  


Explain about SOURCING & SINKING concepts in PLC to field sensor wiring ?

4 Answers   GATE,


1.how can calibration temperature transmitter and flow transmitter? 2.

0 Answers   Gulf Jobs,


waht is difference between pressure transmitter and transuducer

4 Answers   Gasco,


which is the best type to measure level of a Tank(water). Displacer or Differential Pressure method?

2 Answers  


Turbidity analyzer working principle ?

0 Answers   Tata Steel Limited,


Explain about signal isolator

1 Answers   TCS,


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)