132 KV TRFO BUSHING BURNT WHEN A 6.6KV HAS BEEN APPLIED
TO IT .WHY .ANY REASON ?
Answers were Sorted based on User's Feedback
Answer / dinesh lokhande
Let us first understand type of bushing.
Bushings for 132 kV class transformers are generally OIP
(Oil impregnated paper)bushings. However before charging
transformer air release to be done from tranformer tank and
bushings to release trapped air during oil filling. If in
any part of bushing air is trapped then air gets ionised
and provides a path for voltage beakdown resulting in
brsting of bushing due to high voltage stress in bushing.
Some other reason may be dielectric brakdown due to ageing.
Additional information.
Capacitance Tan delta test for OIP bushings can provide
readings of capacitance and tan delta which are indicative
of bushings deilectric health.
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / sathishbabu t
132kv(hi voltage,low current) has less rated current
capacity bushings, if we applied low voltage 6.6kv(low
voltage,hi current) bushing cant withstand hi current.
hence bushing burnt.
| Is This Answer Correct ? | 12 Yes | 5 No |
what is transformer tap change HT side and LT side
EXPLAIN WORKING PRINCIPLE OF ALTERNATOR & MOTORS.
How to design a Unit auxiliary transformer for a power house having a unit of 65 MW and Generating voltage of 11 KV and Secondary voltage of 433V
What are types of HT Motors.
what is the difference between VARIAC,AUTO TRANSFORMER,DIMMERSTAT.
how can we find thae value of capacitor for single phase motor. what is difference between starting capacitor and running capacitor.
difference between earthing and grounding?
why neutral busbar size is SAME of the phase busbar size UPTO 200A IN LT PANELS
What kind of preventive maintenance are there for AC generator?
An 11kv system consisting of an underground cable to a sub station about 300 meters away was shut down for about 10 hrs. On energising, it tripped off on earth fault about 10---20 mins later 6 times but since than it is not tripping.its already 3 weeks now. The SPAJ was found to be fine. what could be the cause.No test had been done to determine the cause of the trippings till now because of demand.
which gas is cost wise high?
What will be the fault current of any system when its generation is 10% of BASE generation( FUll Load )?Will is 10% or the same as full base calculation?
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)