132 KV TRFO BUSHING BURNT WHEN A 6.6KV HAS BEEN APPLIED
TO IT .WHY .ANY REASON ?
Answers were Sorted based on User's Feedback
Answer / dinesh lokhande
Let us first understand type of bushing.
Bushings for 132 kV class transformers are generally OIP
(Oil impregnated paper)bushings. However before charging
transformer air release to be done from tranformer tank and
bushings to release trapped air during oil filling. If in
any part of bushing air is trapped then air gets ionised
and provides a path for voltage beakdown resulting in
brsting of bushing due to high voltage stress in bushing.
Some other reason may be dielectric brakdown due to ageing.
Additional information.
Capacitance Tan delta test for OIP bushings can provide
readings of capacitance and tan delta which are indicative
of bushings deilectric health.
| Is This Answer Correct ? | 14 Yes | 2 No |
Answer / sathishbabu t
132kv(hi voltage,low current) has less rated current
capacity bushings, if we applied low voltage 6.6kv(low
voltage,hi current) bushing cant withstand hi current.
hence bushing burnt.
| Is This Answer Correct ? | 12 Yes | 5 No |
what is meant by surge? what we called for high currents?
why the vector group of excitation transformer is YD5(150 deg)how is this factor decided.
IF I KNOW THE AREA OF CROSS SECTION OFTHE WIRE , WATTAGE OF THE LOAD ,VOLTAGE SUPPLY WHAT IM GIVING TO THE LOAD AND ALSO POWER FACTOR OF LOAD ....... SO GIVE ME FOR WHAT AMOUNT OF CURRENT I SHOULD USE WHICH TYPE OF CABLE?
Plz tell me how we can find that particular company has vacancy or not
how a generating station can monitor its multi users power factor. What type of incentive /penalty is associated with power factor management.
why the Current transformers secodary is shorted to ground (In metering and Protection)
when measure the core loss of three phase distribution transformer or three phase reactor loss, one phase shown negative watt loss. why??
What is the correct procedure to shutdown VCB in 11kv substation.safety and work procedure
Why Closing coli supervision is not required for Circuit breaker.
what are the main differences of delta and star connection
why the power factor is low at no load?
What are the roles and responsibilities of electrical engineer in cement plant
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)