how we can select a transformer based on a particular load.
suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p
& 100 h.p. then what rating of transformer we can select.
urgent. pls reply
Answers were Sorted based on User's Feedback
Answer / mayank goel
40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
Power Factor@.7=287KVA
Loading on Transformer 85%=337KVA
So we can use 400KVA transformer for this motors is okey.
Is This Answer Correct ? | 23 Yes | 0 No |
Answer / eng. ahmed esmail
total HP = 40 + 50+80+100=270HP
1HP=0.746KW
total Kw =201.42Kw
at 0.75 power factor
P= S *P.F
S=268.56 KVA
at 0.85 transformer loading
S=268.56/.85=315.95 KVA
so we will use 400 KVA transformer for this motor loads
Is This Answer Correct ? | 12 Yes | 2 No |
Answer / rahul
=40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
So we can use 250KVA transformer for this motors.
Is This Answer Correct ? | 18 Yes | 10 No |
Answer / ramesh behera
Here the g0hpiven motor values are
40HP,50HP,80HP,100HP
so total HP of motors are
40+50+80+100=270hp
1hp = 746watt
so 270*746=201420w
or 201.42kw
201.42*.85=251.744kva
Some power in hand so we should use 260kva single phase
transformer for these motor load
Is This Answer Correct ? | 4 Yes | 3 No |
Answer / suber
approxmatle 300kva tfr futter add and the load so 333kva
the ans
Is This Answer Correct ? | 4 Yes | 11 No |
Answer / jitesh
=40+50+80+100
=270kva
=362 kw
=270+(270*50%)
=400approx = 500kva X'mer
Is This Answer Correct ? | 3 Yes | 15 No |
How will you calculate the correct KWH value if your CT is 600/5 and your KWH meter is rated for 100/5
What is the automatic voltage regulator with servomotor?
what is the disadvantages of common earthing for AC and DC equipment? (i am talking about inverter control room and inverter duty transformer earthing is common...?)
UPS battery Back time = no.of Batteries * Ah of the Battery / output KVA * 130 ? what is the 130 means ? can any one help? because all are using this formula how its came 130?
How much sq,mm cable need for 800 amps load
while calculating demand in my company the present load in kw is 212.... there 125kvar capacitor bank is installed by spliting as 50 in departments...the diasplay in panek biard shows 175kw... how could we know the amount of kvar used to compensate the kva
Why transformer rating in KVA? and Generator also?
6 Answers Bhel, IEEE, Toyo Denki, Toyo Engineering,
internally connection of photvoltic module
Why the core in the distribution transformer is in even number
what is derating factor in Cable ? how we minimise this?
18 Answers Bhel, College School Exams Tests,
how to find the resistance
what is lrs tank water resistance.