how we can select a transformer based on a particular load.
suppose we have 4 motors of rating 40 h.p , 50 h.p, 80 h.p
& 100 h.p. then what rating of transformer we can select.
urgent. pls reply
Answers were Sorted based on User's Feedback
Answer / mayank goel
40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
Power Factor@.7=287KVA
Loading on Transformer 85%=337KVA
So we can use 400KVA transformer for this motors is okey.
| Is This Answer Correct ? | 23 Yes | 0 No |
Answer / eng. ahmed esmail
total HP = 40 + 50+80+100=270HP
1HP=0.746KW
total Kw =201.42Kw
at 0.75 power factor
P= S *P.F
S=268.56 KVA
at 0.85 transformer loading
S=268.56/.85=315.95 KVA
so we will use 400 KVA transformer for this motor loads
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / rahul
=40+50+80+100
=270HP
1 HP=746Watt
270HP=201.42KW
So we can use 250KVA transformer for this motors.
| Is This Answer Correct ? | 18 Yes | 10 No |
Answer / ramesh behera
Here the g0hpiven motor values are
40HP,50HP,80HP,100HP
so total HP of motors are
40+50+80+100=270hp
1hp = 746watt
so 270*746=201420w
or 201.42kw
201.42*.85=251.744kva
Some power in hand so we should use 260kva single phase
transformer for these motor load
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / suber
approxmatle 300kva tfr futter add and the load so 333kva
the ans
| Is This Answer Correct ? | 4 Yes | 11 No |
Answer / jitesh
=40+50+80+100
=270kva
=362 kw
=270+(270*50%)
=400approx = 500kva X'mer
| Is This Answer Correct ? | 3 Yes | 15 No |
what is meant by negative conductor?
What is mathematical model of a control system?
What is the max demand on your transformer and your company?
10 Answers Bhel, CBRE, Core Consultants, HPL, IOCL, JLL, L&T, Lemon Tree, MNC, Rashmi, TATA, Tata Motors, Tata Power, Torrent Pharma,
can we run all LT motors at 360 volts which are normally rated 415+/-10% voltage rating
what happens when a dc shunt motor fed with an alternating suppy ?
Why there are semi conductor layers on conductor and XLPE insulation of HT cables
whose the first invented AC voltage or DCvoltage
What is difference between dc three point starter and dc four point starter?
wat is power factor
what is the difference between phase and neutral?
3 Answers IAF, Indian Airlines,
1.Can we use 6.6/11KV 300sq mm xlpe 3core cable for LT use (415 Volt). 2. If we use it for LT then what is the current rating
how to select correct size of power cable for inverter duty motor
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)