can we run a motor rated 50Hz,415vac,1440RPM At higher speed
then rated on name plate with the help of VFD /drive on long
term basis.wheater it will effect the motor life
Answers were Sorted based on User's Feedback
Answer / venkatesan.j
Yes the motor can be run above the rated speed through a
VFD ,but it depends upon the manufacturer specification how
much duration and how much it can be raised.
Is This Answer Correct ? | 4 Yes | 0 No |
Answer / farooq malik
VFD varies the frequency of the motor from 0 to 100 persent
at the same time varies the power of the motor. Maximum
frequency it can go up to, is 100% which is 50 hz (Supply
frequeny). so the full speed is at 100 % freq, (that is at
50Hz)which as per name plate is 1440. hope this helps.
Is This Answer Correct ? | 0 Yes | 0 No |
Answer / m bilal akram
yes we run motor long time with use of VFD because VFD
maintain V/F ratio every time.
Is This Answer Correct ? | 0 Yes | 0 No |
What determines the thickness of the lamination or stamping?
We have 420volts, Diesel gen-sets each 750kva 4nos. we are operating with bus bar duct having 10x150mm for each face 4nos. our question is what is the minimum gap required between each face? is there any satutory regulations?
1) What is difference b/w impedence relay and differential relay? 2) what are substations equipments? 3) what is difference b/w circuit breaker and isolator? 4)what are the types of circuit breakers? 5) which medium is mostlty used in circuit breakers and why it is used?
Hi,Any one has idea regarding the KPTCL Recuirtments for AE'e & JE's for the year of 2009-10???Kindly help in regards..
in our 6.6kv motor feeder[it is having two sources from Bus A&B] earth fault relay is acting, we checked CBCT connection and cable meggerd values found very good still earth fault acting during first two are three start after that it will hold. please clarify what was the reason. if same motor is starting from other Bus-A it will start.
why is the vector group analysis done in transformer tests
28 Answers K K Rao, Lloyds, Nicco Engineering Services Limited, Qatar Petroleums,
How to calculate per unit impedance of transformer?
draw tube light circuit
hi!!! i have a question that how the thermal test in winding temprature test is taken can anyone explain me in detail??? i will b very thankful!!!!
why r use the wave taper in the substation ?
Why not LED burn after showing alarm,as Alarm volt is 11- 13,But LED is of3 volt,why it isnt Burn??
why generally transformer are in star to delta or delta to star used?