How calculate the Transformer Impedence With Example
Answers were Sorted based on User's Feedback
Answer / viswakumar
% impedance is the voltage required to circulte full load
current in both HV and LV windings when the terminals of
the LV winding is shorted. This is just the SC test done
in the college lab.
For example if 5 % of 11KV circultes full load current in
the both 11KV side and 415 V side of a 11KV/415 volt
transformer then the % impedance of the transformer is 5%
| Is This Answer Correct ? | 2 Yes | 0 No |
Answer / abdulsubur
1000kva trasformer
1000/root3*.4=1445A=I flow in secondary current
400*5.75%=23
23/1400=.2 0hms
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / abdulsubur
impedence of trasformer = rated kva\root 3 *secondary
voltage
| Is This Answer Correct ? | 0 Yes | 5 No |
only some transformers and some generator requires NGR why?
What is the function of PMG in DG sets & how it works??????????
Why 3 over-current and 1 earth fault relay is used on primary side of transformer? Why 2 over-current and 1 earth fault relay in used on secondary side of transformer?
In dc ckt. 24v or 110v, which one is more efficient and why?
can anybody send me syllabus of rrb section engg (electrical). and also send previous question pepar...
I have 4 busbar of 1000 ampere. we use 4 busbar to make 4000 ampere in one phase.my problem is that when we applied 60% load on that then busbar produced high noise.what is the reason of that and how can i minimize that noise.
0 Answers College School Exams Tests,
why dc power can not be used in transformer?
33 Answers GE, Sail,
how to calculate the minimum permissible limts of insulation resistance of switchyard equipments
i have one source transformer with the capacity of 50KVA, connected with two loads 10kw and second one is 15kw.. how can i calculate first load in KVA and second one in KVA .. because Kva rating, power factor rating of of transformer is different from the load… there must be some way to calculate load KVA rating and power factor….
As per IS why should the control be taken only from R phase, why not from B or Y phase??!!
what are the disadvantages in GIS over AIS
Define peak overshoot.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)