What is the Frequency while we step up the voltage from
220V to 11KV? Is it possible? Explain it?
Answers were Sorted based on User's Feedback
Answer / shan80
The working principal of transformer is step up / step down
voltage without any chage in frequency.
So frequency remains same at both sides step up side or
step down side, normaly it is 50Hz.
| Is This Answer Correct ? | 19 Yes | 0 No |
Answer / fransis
Generally Frequency is maintained by generation station for
a common distribution system.It is not possible to change
frequency while step up or step down the voltage on any
transformer.
This is also possible to change the frequency by term of
electronic controll device like in soft starter. In the soft
starter frequency is controlled with voltage to control the
speed of motor.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / parin
it is possible to step up 220v to 11kv using transformer,transformer does not change frequency,ti only transfer power one stage to another with constant freq.
| Is This Answer Correct ? | 3 Yes | 0 No |
Answer / amarnath
it should be or it is 49.5 to 50.5 Hz normally. If this is
not the frequency then we need to have a capacitor to
improve the frequency and power factor.
| Is This Answer Correct ? | 2 Yes | 1 No |
Answer / rahul
frequency is same that of 220kv,220/11kv is possible.it
depends on secondary windings
| Is This Answer Correct ? | 0 Yes | 0 No |
Answer / azhar ali
It doesn't matter if you step up or step down the voltage, frequency will always remain the same as per principle of transformer it transforms voltage without any change in frequency.
| Is This Answer Correct ? | 0 Yes | 0 No |
Why one can experience electrical Shock due to Voltage or Current?? or both voltage or current??
what is feeder bay?
What is diode fuse ? How it is working?
In winding design, the angle of chording (β) is nearly equal to A 45 degree B 60 degree C 30 degree D 90 degree
What is meaning of star delta connection / delta star connection and which one is best and what is the advantage?
140 is load amps for a equipments and what ratio of CT requied for installimg ammeter to amps montering purpose?
how a circuit breakers work at fault condition .plz give a specified answer.
IF we want to replace I/C bay at our 220 kv substation which is of 140 mw load capacity bay to be replaced by 400 mw capacity bay.other than CT(1200/1) what are the other equipment i have to replace.
what is the current setting for different relay protection for transformer .
Why using synchronising methed in DG's sets?
i am going to correct power factor of 1600kw induction motor,when i calculate capacitance of capacitor it is three time more in star connection than delta. if motor is star connected which connection i shall adopt for capacitors and reason for adopt this connection
what is pmu
Civil Engineering (5086)
Mechanical Engineering (4453)
Electrical Engineering (16638)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)