In which connection the voltage will be more , in star or
delta connected motor?
Answers were Sorted based on User's Feedback
Answer / shan80
in star connection line voltage =total voltage/1.732
and delta connection voltage lline voltage =toltal voltage.
thats why in delta connection voltage will be more then
star connetion.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / mohammed rafi
all aforesaid answers are absurd or partially mistake.
Both delta connection and star connection has same voltage.
But star connection gives the provision to tap a separate single phase connection which will be of course lower voltage.
For example- In India,existing 3 Phase supply is 415V (10% deflection is permitted). You can obtain it either in the form of delta connection or star connection.
The single phase connection (230 V)which you receive in your home is actually a taped connection taken from star connection. A star connection will have 4 wires,there are R phase,Y Phase, B Phase and Neutral. Voltage between R-Y and R-B and Y-B or any phase to phase combination is 415 V
Now if you take a phase,let it be R or Y or B and check it's voltage w.r.t neutral,it will be 230 V. This is known as single phase voltage.
Delta connection has only 3 wires,they're R,Y,B and there is no neutral. So You cant tap a single phase from a delta connection directly.
This is the difference between star and delta connections. Moreover its worth to mention that question which triggered all these discussion is wrong. Because,now you have understood both has same voltage but the only difference is you can tap a single phase connection from a star connected supply.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nataraj c - voltech engineers
In Star Connection or Delta Connection, The Voltage will be Remains Same, Only thing is the connection of the motor or transformers which ever it may be is different.
The purpose is for the changing connection is to limit the starting current of a motor. in star connection the current is limited by 1.732 times less then the delta connection.
| Is This Answer Correct ? | 1 Yes | 7 No |
How to calculate main incomer rating of APFC Panel ? Let's say i want to find main incomer for 11kV, 1000kVAR Panel.
how to find Harmonics and types as per the equipemnts
what is the meaning of Air condition "TON"
How to calculate ht side cable of 630 kva oil cooled outdoor transformer?
i alternator which of genarator used for excitor the what is reason?
Please provide me detail cable voltage drop calculation
describe the Tranformer testing procedure
Why electricity is generated and transmitted at the values of multiples of 11?
How neutral voltage for transformer decided? eg 33kv neutral voltage for 200MVA transformer?
What is mathematical model of a control system?
can someone explain that how the speed of the protection system affects the fault level calculation?
what is mean by busbar and what is the difference between busbar,transmissionline,feeder,distribution line
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)