In which connection the voltage will be more , in star or
delta connected motor?
Answers were Sorted based on User's Feedback
Answer / shan80
in star connection line voltage =total voltage/1.732
and delta connection voltage lline voltage =toltal voltage.
thats why in delta connection voltage will be more then
star connetion.
| Is This Answer Correct ? | 12 Yes | 2 No |
Answer / mohammed rafi
all aforesaid answers are absurd or partially mistake.
Both delta connection and star connection has same voltage.
But star connection gives the provision to tap a separate single phase connection which will be of course lower voltage.
For example- In India,existing 3 Phase supply is 415V (10% deflection is permitted). You can obtain it either in the form of delta connection or star connection.
The single phase connection (230 V)which you receive in your home is actually a taped connection taken from star connection. A star connection will have 4 wires,there are R phase,Y Phase, B Phase and Neutral. Voltage between R-Y and R-B and Y-B or any phase to phase combination is 415 V
Now if you take a phase,let it be R or Y or B and check it's voltage w.r.t neutral,it will be 230 V. This is known as single phase voltage.
Delta connection has only 3 wires,they're R,Y,B and there is no neutral. So You cant tap a single phase from a delta connection directly.
This is the difference between star and delta connections. Moreover its worth to mention that question which triggered all these discussion is wrong. Because,now you have understood both has same voltage but the only difference is you can tap a single phase connection from a star connected supply.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / nataraj c - voltech engineers
In Star Connection or Delta Connection, The Voltage will be Remains Same, Only thing is the connection of the motor or transformers which ever it may be is different.
The purpose is for the changing connection is to limit the starting current of a motor. in star connection the current is limited by 1.732 times less then the delta connection.
| Is This Answer Correct ? | 1 Yes | 7 No |
What is the major differences between RCCB & ELCB? If we use ELCB of less sensitivity why does it trip often and can we control it from tripping?
What is the height of DA, DAL, DB, DC & DDE tower?
Can anyone explain the power flow in flouresent lamps (tube lights) .What are the functions of Starter & choke used there?
Is it necessary to place tap changer in secondary winding or we can use on both sides?
hi i have a 400kva transformer i want to know the test i can use to check on it thx
If we need4× 50mm sq cable but it's not available so we can pull 4×25mm sq 2cables
What is Procedure the procedure to select CT's & PT's in 66kV and above substation?
What can you contribute to the progress of our Company as an employee if you are selected?
WHAT IS THE DIFFERENCE BETWEEN SHOP DRAWINGS/ DESIGN DRAWINGS AND AS BUILT DRAWINGS??
2 Answers ACC, Al-Jaber, Dubai Group, ECEC,
if we have a industrial load of 400 kilowatts with 415 volt AC then how much total harmonic distortion (thd%) should be acceptable for steady power system.
Is there is any hazard to insulation of 3hp motor 5 KV megger is used for it?
what is relation between HP & BHP
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)