Why Two Transformers aside shoud be supperated by concreted
wall?
Answer Posted / tom hanks
Any two transformers in a plant/substation are always
seperated by a concrete wall known as BLAST WALL, (Blast
walls are generally 1000mm+ bigger the size of larger
transformer) It is protect the healthy transformer from
fire, incase the other one is on fire due to short-
circuit/oil leakage etc.
| Is This Answer Correct ? | 6 Yes | 1 No |
Post New Answer View All Answers
Why frequency changes due to load variation in power system ? i.e why when load increases frequency decreases?
what happen if generator of micro hydro running at only a small percentage of its capacity, as a comparison, if the diesel generator that runs on only a fraction of its capacity there will be a wet stacking
how to ctrl motor by use of ac or dc drive.plz explain evdintly
What do you mean by a phase angel of instrument transformer?
oil cooled transformer
why star point of HT motor not earthed?
What is a copper loss or i2r loss pc?
what is sustainable current of any conductors . a bare busbar or pvc cable has different sustainable current .
I have 1500/1A CT If i connect this CT in 6.6KV bus bar means what will be the voltage present in CT?
Can we use BS 6651 and BS EN 62305 standards for computer room lightning ptotection in substation?
l&t switch FN 63 handle position can we change
What is milivolt dop test in Busducts? What is its significance & procedure to do the test?
What is the Difference between Ac Drives and Dc Drives? According to application, speed, Torque, cost, Reliability, Construction, Motor etc... Thankyou !!!
Can anyone explain me about the capacitor calculation
What is Scheme Test of High Voltage Switchgear. Which tests it includes.