if the t/c o/p is 4-20mv then how plc recognize it
because we are dealing with the 4-20ma in the
plc ????????????????
Answers were Sorted based on User's Feedback
Answer / arindam
why we require a 4-20 mamp for transmission? the main reason
behind it because of electro magnetic interference the
voltage can get interfered very easily and we can't get our
desired o/p value.when we are using 4-20 mamp this problem
is solved but since, PLC is a digital device it can
understand mainly High=5V or low so we design the sink to
have a resistance as high to get the desired voltage, the 4
mamp is also helpful to power the electronics at the
transmitter end. to have a 4-20 mv instead can firstly :
cause em interference and secondly we need to have a
continuous level monitoring for different voltages...which
can increase the size of PLC . Also because of change of
impedance at the transmission line the voltage can drop
below 4 volt ocassionaly then loop powering of field
instrument will not be possible.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / biswarup das
There is different module in a PLC . Out of which one is T/C
module if you connect the o/p of T/C directly to this module
of PLC , then the PLC will recognise it.
T/C module is not inbuilt we have to select it seperately.
There are many modules like this such as RTD module, 0-10
volt module etc.
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / guest
we will convert mV in to the ma....by connecting resistance
in parallel
Is This Answer Correct ? | 5 Yes | 4 No |
Answer / sreekanth
standard thermocouple output is 0 to 10 mV. There will be 4-
20MA converter either in DCS in the field(Transmitter)as
the modules will accept only 4-20 MA output.
Is This Answer Correct ? | 1 Yes | 5 No |
How can you convert an SR Flip-flop to a JK Flip-flop?
IF ASK IN THE INTENVIEW WHAT TYPE OF BMS YOU USE?
What is a PID?
if conical type tank in top LEFT side solid material coming but LT MOUNTED IN TOP OF LEFT SIDE, how to measure ultrasonic level transmitter ?
PID controller is used for which type of compensation…… a) lead comp. b) lag com. c) lead lag com.
12 Answers Engineers India Limited,
WHAT IS THE CAM POSITION IN CONTROL VALVE POSITIONER ? WHY IT IS USED?
What is the relationship between GAIN and PROPORTIONAL BAND.
1 Answers Kharafi National, Sabic,
i install a DP transmitter of Faugi on drum level of boiler but i face a problem in it when i engergize the transmitter the meter shows 0 or 100% no variation in it.the distance of two points is 19.5 inches, i am in trouble please suggest me what can i do it's very urgent Please reply me as soon as possible Best regards ikraam haider
give eg of how I/P is used in control loops
how level can be measured in open tank with reference to pressure
Can we use a 10000 Lph Flow Transmitter in 100 LPH flow line to get 20mA O/P by adjusting SPAN ?
what is the difference between -24 : +24 & 0:24 and where it use?