My rtd working well at the same time r/i converter is not working properly.when power is given to rtd..it is giving 30mA and getting 2.4 mA if i remove the compensate leads No matter how many ohms.why it is happening like so?what is the solution?rtd range-0-200deg c& 4-20 mA o/p.please give me solutiin anyone......
Answer / carl_ellis
Any 2 wire, loop powered 4-20mA transmitter that puts out
30mA is broken. The only transmitter that puts out 30mA is
a legacy 10-50mA transmitter from 20-30 years ago.
While the upper end of the 4-20mA signal range is 20.0mA,
most 2 wire, loop powered transmitters allow for some slight
signal over-range, typically 20.5mA.
NAMUR standards use 21.0 mA to signal a fault or failure
mode. Other vendors use other values, 20.8mA, 21.2mA or
some value in the range of 21mA. But no vendor uses 30mA
as a fault mode.
The transmitter is broken or dysfunctional.
Carl Ellis
Measure First
Is This Answer Correct ? | 5 Yes | 0 No |
Paper Details: company -- Hindustan Copper Limited post -- GET 2008 Date -- 03.08.2008 Dept.-- Electronics?Instrumentation Aptitude -- 70 Technical-- 80 Total Time -- 2hr 30min I have listed the question I could able to remember 1. BCD equivalent of 43 2. value of K for stability of a system from a given equation 3. transformer connection for darlington connection 4. damping of balastic galvanometer 5. advantage of chart-pen recorder over CRo 6. CRO - how to change bandwidth 7. questions on CRO construction 8. reverse saturation current of si diode 9. advantage of wire wound resistance over carbon resistance 10. core material for a small coil 11. max fanout-- TTL/ECL/CMOS/MOS 12. component of resistance of monolithic IC 13. functions of capacitors in multivibrators 14. to change a sawtooth signal into a square wave we use-- schmit trigger/ schottkey diode/ zener diode 15. relation b/w á & â in transistor ckt 16. function of SiO2 layer in fabrication 17. 3 questions on ODD MAN OUT
What is furnace draft control?
Will Intergraph support SmartPlant Instrumentation in an AutoCAD or MicroStation environment on a long-term basis?
THE OUTPUT OF A CURRRENT TRANSMITTER OR A PNEUMATIC TRANSMITTER HAS A LIVE ZERO?EXPLAIN
What is open loop checking and close loop checking
what does it mean an active front end in vfd plz explain it briefly
What is the difference between a Extension cable and a copnesating cable.Where can we use compensating cable. Is anywhere compensating cable are used for mv transmission to the indicator.
what is the difference between(Flame proof/Explosion proof)& Fire proof instruments.Both are same or different & if different in which way because the transmitter which have approved ATEX flame proof enclouser but it use PTPE O ring & PTFE Head Gasket,so its (fire safe/fire proof)????????
what is dry leg and wet leg in transmeter calibration?
On liquid service if PT Head is 18 meters. How much pressure will be exerted on it. If Transmitter is not in service?
How much flow is passing through 6 inch line? There are no gauge, no any transmitters in line.
Why trim span ? How?