how we have to calculate the short circuit current for
33/11kv 2mva, 7.5% Z, Transformer primary side breaker and
secondary side breaker short circuit current for both sides?.
Answers were Sorted based on User's Feedback
Answer / sunil ulange hit nidasohi
Sort circuit MVA= Rating * 100 / Z%
Short Circuit Current =Short circuit MVA / 1.732* Voltage
Is This Answer Correct ? | 7 Yes | 3 No |
Answer / karuppannasamy
Rated primary current=2000/(1.732*33)=35A
Short circuit current= Rated current/Impedance
= 35/.075=466A
Similarly
Rated secondary current=2000/(1.732*11)=105A
Short circuit current=105/.075=1400A
Is This Answer Correct ? | 2 Yes | 4 No |
Answer / madhu
Fault impedance in secondary Z = %Z x 10 x (KV)²/KVA
= 7.5*10*11*11/2000
= 4.5 OHMS
then fault current in sec = V/(Z*1.732)
= 11000/(4.5*1.732)
= 1411 A or 1.4kA
similarly in primary Z = 7.5*10*33*33/2000
= 40.83
then fault current in prim = 33000/(40.53*1.732)
= 0.466kA
Is This Answer Correct ? | 0 Yes | 3 No |
How many types of instrument cables are there?
Dear sir, How to calculate 3.5 core pvc aluminium armoured cable meter wise,give with best examples.... please help me in this regards....
what type of current supply is given to house holds?
when voltage increases then current also increases then what is the need of over voltage relay and over current relay? can we measure over voltage and over current by measuring current only?
For Electrical / and Electronic Systems, when we say efficiency is 80%, then what happens to other 20% from the Power consumption.? I.e. what happens to this?
Spacing of Transformers ratings are 10kva,15kva,25kva,63kva,110kva,150kva .........so on Q) Why transformer are not manufactured having ratings in between or other than these standard ratings ?
which turbine has high thermal efficiency a)open gas turbine b)close gas turbine
In 3 phase induction motor even with low Voltage it reaches nearly it's rated speed why? (for example instead of 400V it reaches with 250V)
hey guys help me out.....what are the industrial uses/functions of nozzles in industries
What are steps to be taken while designing of DYN11 distribution transformer to achieve magnetising balance?
What is reason of rating of transmission line multi pal of 11 like as 11/33/66/220 ? Why not use 75 kv 23 kv line in power system ?
1 Answers Apollo, Balco, Bhel, Vardhman,
In AC if the direction of current keeps reversing every half cycle, how does it propogate through the transmission lines?