what is work of CTPT in 33/11kv Substation
Answer / rich sawe
CTPT - The Current Transformer and Potential Transformer,
these are instrument transformers used mainly for high voltage instrumentation purposes at the substation
1.Measurement purposes;these transformers provides low level signals to the metering equipments to measure line voltage level and line currents at the substation.
2.Protection purpose;these transformers provides signals to the upon occurrence of fault , over-current and under-current faults are firstly sensed by the current transformers then signals the O-C/U-C RELAY to trip the Circuit breaker ,Over-voltage and under-voltage faults is firstly sensed by Potential Transformer then signals the O-V/U-V RELAY to trip the Circuit breaker.
3. The occurrence of unbalanced fault condition in three phases at the substation is detected by the current transformers and potential transformers and the signal is fed to the respective relay to operate the circuit breaker.
4.on the POWER GRID the performance and operating status of the HIGH VOLTAGE SUBSTATION are monitored and controlled through feedback from CTPT
...DIT TANZANIA...
Is This Answer Correct ? | 7 Yes | 2 No |
How to calcualte 1unit of current consumption?
3 Answers Bhushan Power Steel, ITC Infotech,
Railway Basic electrical engg technical question with answer
HOW DG WORKS ?
Can 60 Hz transformer be used inplace of 50 hz transfromer?
what is the diff between earth leakage relay and earth fault relay?
how much kn lightning arrestor is used in 11kv line
toughest decision you ever had to make
Iwould like to know barc interview questions
what is mean by amf
while doing high potential for 11KV 3 core cable how much leakage current will obtain?, what will be acceptance value?
why induction motor takes high current?
Explain the working of variable frequency transformer?