how to calibrate transmitter
Answers were Sorted based on User's Feedback
Answer / binosh
pressure transmitter:
in bench calibration connect a power supply 24v.give a
250ohms as loop resistance.connect a multimeter in
milliamph mode and connect it in series.and put a
communicator across the loop.the transmitters HP&LP sides
should be in open to atmosphere.this condition the
ammeter shows 4ma and the communicator shows LRV .connect a
pressure calibrator to the HP side and LP keep it open to
atm.apply pressure as the range and go on as 25%,50%,75%and
URV.then the ammeter shows 4,8,12,16,20ma
respectivly.incase you are not getting zero,make zero trim.
Is This Answer Correct ? | 7 Yes | 1 No |
Answer / s. kanniyappan
TEMPERATURE TRANSMITTER:
GIVE 24VDC TO THE TRANSMITTER
CONNECT MULTIMETER IN SERIES WITH -VE TO THE TXT
GIVE RESISTANCE INPUT TO THE TRANSMITTER
GIVE LRV VALUE BY ADJUSTING THE DRB
ADJUST ZERO FOR LRV
GIVE URV VALUE BY ADJUSTING THE DRB
ADJUST SPAN FOR URV
GIVE 25%, 50%, 75%, 100% OF URV (RESISTANCE) AND CHECK THE
CORRESPONDING MILLIAMPS OUTPUT
PRESSURE TRANSMITTER:
GIVE 24VDC TO THE TRANSMITTER
CONNECT 250 OHMS IN SERIES WITH -VE TO THE TXT
CONNECT THE HART TO THE TERMINALS OF RESISTANCE
CONNECT THE TRANSMITTER TO THE SOURCE VIA REGULATOR AND MAKE
A T OFF CONNECT TO A MASTER GAUGE
VARY THE PRESSURE BY ADJUSTING THE REGULATOR
MAKE ZERO TRIM FOR ZERO PRESSURE THROUGH HART
ADJUST THE REGULATOR AND CHECK FOR THE LRV VALUE IF NOT
MATCHING ADJUST THE ZERO
DO THE SAME FOR THE URV
GIVE 25%, 50%, 75%, 100% OF URV (PRESSURE) AND CHECK THE
CORRESPONDING MILLIAMPS OUTPUT
DP TYPE TRANSMITTER
LP LINE SHOULD BE LEFT OPEN TO ATMOSPHERE
CONNECT THE HP LINE TO THE SOURCE AND DO THE SAME AS ABOVE
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / rajkumar
Any Txr has input, output, supply. give the simulated input
ie.. mA source or mV or pneumatic and check the o/p. if o/p
doesn't match adjust zero or span . Have details of range of
measurements in hand. In need use them also to get desired
output
Is This Answer Correct ? | 6 Yes | 8 No |
given a processor batch of 1000 resistors moving on the conveyor belting in a large factory. the resistors is value at 10k ohms each but when the resistors reach the quality control, some of the resistor has been rejected caused by failure in manufacturing.the high quality measurement is used to determine the failure. describe the instrumentation terminology in measurement of a system above with explaining the important in:- -reliability -sensitivity -repeatability -precision -range -resolution -linearity -hysteresis -error -accuracy (answer must related to the scenario above)
What is the input impedence of an OPAMP as an ideal device.
When we will do simulation for I/P?IF WE DO SIMULATION through which way either series or parallel?
can i get any detail of interview question asked for instrumentation,plc,scada ,dcs..............
Where we cant instal mass flow meter.
explain Cascade Control strategy with the help of a block diagram. also exlain its working in a distillation column
how is hazardous and non hazardous area classified?
2 Answers Bhel, Power Plant, Samsung,
our kks tagging is crossing more than 12 character please suggest how to take tags in the DCS
What information needs for Control Valve "sizing"
can we create an interrupt in plc through scada?
How to Calibrate Ultrasonic flow Transmitter in Field
WHAT IS THE DIFF. BETWEEN SKIN TEMPERATURE AND PASSES TEMPERATURE..?