Answer / omar aziz
ELCB= Earth Leakage circuit breaker
RCCB= Residual current circuit breaker
elcb looks for current flowing in the earh wire and is it
does not equate to the phase current , earth leakage is
detected an the CB trips.
rccb looks for the residual current ,by adding the phasor
current . upon any imbalance the CB trips on residual earth
fault.
| Is This Answer Correct ? | 26 Yes | 3 No |
Answer / k.rajeesh
ELCB= Earth Leakage circuit breaker
RCCB= Residual current circuit breaker
elcb looks for current flowing in the earh wire and is it
does not equate to the phase current , earth leakage is
detected an the CB trips.
rccb looks for the residual current ,by adding the phasor
current . upon any imbalance the CB trips on residual earth
fault.
| Is This Answer Correct ? | 12 Yes | 0 No |
Answer / velusamy
The ELCB works on the principle that the total amount of
current flowing thro the phase is returned thro neutral. if
not so , elcb trip the circuit.
For RCCB, i agree with ans 1 & 3
| Is This Answer Correct ? | 9 Yes | 0 No |
Answer / karthik
RCCB: detects current imbalance.but does not provide over
current protection.
ELCB: detects earth current directly rather than detecting
imbalance.
| Is This Answer Correct ? | 6 Yes | 1 No |
Answer / vinodh.t
ELCB= Earth Leakage circuit breaker
RCCB= Residual current circuit breaker
both are same..the objective of elcb is continuous
monitoring of insulation levels of electrical installation
and equipments and also detect any leakage current flow to
earth
| Is This Answer Correct ? | 8 Yes | 15 No |
Transformer's core is made up of which material and why so?
How we calculate the size of H.T cable for any transformer & rating of busbar for any L.T. panel?
PLEASE INFORM ABOUT THE IDEAL TEST RESULTS OF MAGNETIC BALANCE TEST OF TRANSFORMER 33/11 kv DELTA-STAR T/F
how can we can take BDV test in transformer?
I have an existing old MCCB. ABB Model SACE, the rating are: Ue = 660 volts, Iu =1250 Amps, 3 poles, Ith (max) =800 amps at 45 deg C. I need a circuit breaker for my 3 phase motors, 380 volts 60 hz. the supplier required the minimum ampacity of the breaker to be 911 amps. can i use this breaker with rating of Iu =1250 amps but Ith = 800amps maximum?
why fuse is not used in neutral...
Can you tell me more about pu systems (per unit systems )calculation in large power systems? how to get the base for voltage and power in generator, transformator and transmission lines?
Dear all, how we select the cable size according to current with or without including different correction factor , is there any direct method for sizing of cable...
what is the use of earthing?
I try to check the three phase voltage in multimeter, in 125A isolator switch incommer. first i touch R phase, and then i touch Y phase using multimeter, the moment i touched, it blasts and that moment i got blindness. multimeter selector position is correct(750V AC MODE AND RED PROBE WASS IN v AND BLACK PROBE WASS IN COM. MODE. COULD ANYBODY GIVE ANSWER FOR THIS TO AVOID FURTHER ACCIDENTS PLEASE?
Why mostly GT(Generating Transformer)has only Ynd1 Vector Group?
Write down the classification of the transmission line?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)