how can we can take BDV test in transformer?
Answers were Sorted based on User's Feedback
Answer / santosh kumar jha
BDV means break down voltage.
This is the test of di-electric strength of transformer oil.
The sample is taken in electrolysis pot and applied a
voltage diff between anode and cathode of the pot , the
diff between the two plate is 2.5 mm.At first we appling
the voltage diff gradually , the voltage near which the oil
looses its insulation property, that voltage is called BDV.
| Is This Answer Correct ? | 157 Yes | 7 No |
Answer / ilononurb
we can take the break down voltage of transformer oil by
using oil tester. Take oil sample of tr oil and put in to
the testing oil pot with the spere electrode of 2.5mm gap.
Applied gradually the voltage till the oil losses its
dielectric stenght. breakdown voltage will display to the
oiltester meter. As per IEC 156 Standards it should be
40kv.eff.
| Is This Answer Correct ? | 78 Yes | 8 No |
Answer / rahul sharma
BDV tests is used to test the dielectric strength of the
transformer.
A new transformer oil shol\uld have at least dielectric
strength of 39 KV as per british standards.
Transformer oil used are normally tested using ASTM D877-82
with the KV strength testing,using 1" electrode spaces 0.1"
apart & test voltage increased at 3000 volts\min until it
breaks down. The avg KV obtained after 8 trails is
considered the oil dielectric strength.
Using this test dielectric strength at 30KV & above is
considered good. Dielectric strength between 23 to 29 KV is
considered usable ,but requires filtering, below 23 KV
transformer oil should be replaced.
| Is This Answer Correct ? | 41 Yes | 8 No |
On TRANSFORMER OIL BREAK DOWN VOLTAGE test is carried out which is done on field while filling the oil in transformer. This process is also called oil filtration.
1.Take sample from top of Transformer before filtration.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test electrodes sample to be 2.5mm maintained
4.At least 5 sample(top/bottom) should be checked separately while filtration.
5. The samples should withstand 50 kv for 1 min.
5. Take the average of all the samples timings.You will get value.
7.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
| Is This Answer Correct ? | 26 Yes | 4 No |
Answer / s.anand
take sample before maintank bottom this coreact methode
| Is This Answer Correct ? | 2 Yes | 1 No |
What are the advantages of speed control using thyristor?
what is the different between counterpoise earthing and pipe earthing?
role of shunt coil in circuit breakers
A cable with concentric PE conductor must be used with frequency converter circuits what does its means.?
why is neccessary Tap changing of power transformer with in a certain time
The control system is used for?
why do we need a 4th wire in 3phase 3wire transmission line
what is the problem in manufacturing transformer with 0 degree phase displacement.???why alwasys go for DYn11 or DY5?Whys not DY0 i.e zero degree displacement between primary and secondary side vectors?
3 Answers Bhel, dpdc, Prime Electrical,
how to test the electrical panel.ht lt mcc pcc.
length of 4 core cable 95mm from substation LV VFD panel to Motor at field approximately 150 meter. Motor stop and power has been isolated from LV MCC ( Substation )to disconnect Motor for services. After Motor completed service propose to reinstall and reconnect Motor Cable, found earth cable sparkling during touching at metal / motor body. Inspect by clamp meter found earth cable have current flow AC 1-2amps and all earth cable at MCC LV also have current flow as same value. why it is happen?
how to calculate the ngr capacity(nutral grounding resistor)
I WANT TO KNOW LONGFORM OF CT/PT USEDIN POWER PROJECTS OR HT SWITCH YARD.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)