how can we can take BDV test in transformer?
Answers were Sorted based on User's Feedback
Answer / santosh kumar jha
BDV means break down voltage.
This is the test of di-electric strength of transformer oil.
The sample is taken in electrolysis pot and applied a
voltage diff between anode and cathode of the pot , the
diff between the two plate is 2.5 mm.At first we appling
the voltage diff gradually , the voltage near which the oil
looses its insulation property, that voltage is called BDV.
Is This Answer Correct ? | 157 Yes | 7 No |
Answer / ilononurb
we can take the break down voltage of transformer oil by
using oil tester. Take oil sample of tr oil and put in to
the testing oil pot with the spere electrode of 2.5mm gap.
Applied gradually the voltage till the oil losses its
dielectric stenght. breakdown voltage will display to the
oiltester meter. As per IEC 156 Standards it should be
40kv.eff.
Is This Answer Correct ? | 78 Yes | 8 No |
Answer / rahul sharma
BDV tests is used to test the dielectric strength of the
transformer.
A new transformer oil shol\uld have at least dielectric
strength of 39 KV as per british standards.
Transformer oil used are normally tested using ASTM D877-82
with the KV strength testing,using 1" electrode spaces 0.1"
apart & test voltage increased at 3000 volts\min until it
breaks down. The avg KV obtained after 8 trails is
considered the oil dielectric strength.
Using this test dielectric strength at 30KV & above is
considered good. Dielectric strength between 23 to 29 KV is
considered usable ,but requires filtering, below 23 KV
transformer oil should be replaced.
Is This Answer Correct ? | 41 Yes | 8 No |
On TRANSFORMER OIL BREAK DOWN VOLTAGE test is carried out which is done on field while filling the oil in transformer. This process is also called oil filtration.
1.Take sample from top of Transformer before filtration.
2.The BDV of oil should withstood min 50 KV
3.The gap between the test electrodes sample to be 2.5mm maintained
4.At least 5 sample(top/bottom) should be checked separately while filtration.
5. The samples should withstand 50 kv for 1 min.
5. Take the average of all the samples timings.You will get value.
7.Procedure
a.Voltage should be gradually increased from 0.
b. At one point Flash will take place and that point is
termed as Bread down Voltage
Is This Answer Correct ? | 26 Yes | 4 No |
Answer / s.anand
take sample before maintank bottom this coreact methode
Is This Answer Correct ? | 2 Yes | 1 No |
i am in need of AC SYNCHRONUS MOTOR 30KW. ANY ONE KNOWS THE MANUFACTURER OF SAME. ALSO MOSFET AC CONVERTER 20KVA CONT.OUTPUT.
There are different classes of protections in power plants.class a,b,c are clear..is there any class d and e r there..and elaborate class b protection.
i had aplied Hindustan Petroleum corporation limited for the post of maintenance technician -Electrical,i want model questions,if anybody have please send it or please advice?
why we calculate only 11kv 33kv and 132kv ... why not 10kv 20kv 45kv?
sir pls tell me . our ct specifications are 120/5 ,2 core , 0.2 and 5p10 class , 30va and 30va buden. insted of 30 va i want use 15 va. can i use?
how to calculate regulation constants for over head lines? and what are the regulation constant for raccoon conductor at different voltage level and different P.F?
what is high tension ? specify the range?
discuss thyrister convertor type of AVR.
in india why 50 hz and 220 volt taken as standard rating for equipments whereas in US 100hz and 110v is consided as standard rating.is this method save power.
in delta connection, why motor rotate in high speed compared to star connection?
what's the exact magnitude of current, flows through Neutral?
What are the factor to be consider for CT selection in 132kV substation?