Answer Posted / k.rajeesh
ELCB= Earth Leakage circuit breaker
RCCB= Residual current circuit breaker
elcb looks for current flowing in the earh wire and is it
does not equate to the phase current , earth leakage is
detected an the CB trips.
rccb looks for the residual current ,by adding the phasor
current . upon any imbalance the CB trips on residual earth
fault.
Is This Answer Correct ? | 12 Yes | 0 No |
Post New Answer View All Answers
How to calculate impedance volt in Transformer?
What is ideal IR values for ground and neutral.
Why we are using Isolation Power Transformer inplace of commercial power transformer? What's the difference between them?
one conductor length is L.and i am strech uniformly this conductor and made length is 2L.so resistance of this strech conductor is R=4R..but i want to know about area of stech conductor hows it become a/2..
Pl. give me checklist for installation & commissioning of machine tool.
what are the effects when a salient pole alternator is run at high speed like 3000 r.p.m?
What is an iron loss or core loss pi?
WE ARE PLACE A NEW 75 KW MOTOR FOR JPF.IT IS CONNECTED IN M.C.C. WHEN WE ARE STARTING M.C.C.INCOMER IS TRIPPED.THEN WE ARE CONNECTED IN P.C.C WITH A MM30 RELAY PROTECTION THEN WE ARE STARTED MOTOR WILL RUN SMOOTHLY.
i need list of swg(standard wire guage) or area of conductor v/s current carrying capacity of conductor copper & alluminium...
i have flexible wire. size of conductors is 0.190 mm & no.of conductors are 48. then size of wire comes 1.37 sqmm instead of 1.5 sqmm . the what is tolerance for this size.
What are the site acceptance tests for power cables, DG Sets, LT panels & 30kVA UPS ?
Can we use Ccapacitive voltage transformer directly for metering purpose?
Safety of on line ups
what will be the effect if you were using different brands of outlets?
how many types control panel of a 132/33 kv substation