what is mean of 3 by 2 automation ?
Answers were Sorted based on User's Feedback
Answer / farooq
if three sensors installed to measure or monitor one process
variable and when two of them give a high or equal to a set
value than an alarm or correcting action can be activated is
called 2 out of 3 automtion.
| Is This Answer Correct ? | 10 Yes | 1 No |
Answer / senthil
for example,consider the three transmitters are in
service.in logic,the three xtr compare each other value i.e
A&B,B&C,C&A. check the diff of deviation b/w the
comparison.the xtrs showing minimum deviation is taken,from
this the mean is taken b/w two xtrs.this is 2 0f 3.
| Is This Answer Correct ? | 4 Yes | 3 No |
Answer / ladla
this information is apply for alarm and trip system where
these shows the redundant of the system
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / senthil
2 out of 3:
for example:
we use three pressure transmitters in the process line
discharge of a pump.consider the range is ( 0 to 10 bar).we
have a condition that when the discharge pressure is low the
pump has to trip(less than 4bar).
-if two transmitters goes below this value there is trip.
we have deviation alarm,deviation deadband warning also in 2
voting 3 concept.
| Is This Answer Correct ? | 1 Yes | 1 No |
Answer / gopi
step by step implimentation our logics by using any controller
| Is This Answer Correct ? | 0 Yes | 1 No |
which type of signal used in instrument?
3 Answers Emco, Makson, Sail, TATA,
What is SCADA ? WHAT is it role in DCS ?
IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB) USING HART COMMUNICATOR.? I MEAN TO CHANGE FROM ONE UNIT TO ANOTHER WITHIN INDICATOR (EG. INCH TO FEET)...? PLZ NOTE THAT I HAVE MADE THE UNIT CHANGE IN TRANSMITTER USING HART COMMUNICATOR..BUT WHAT ABOUT THE INDICATOR..?
How to convert milliampares into flow??
How DP Transmitter can be calibrated for crud application in floating roof tank?
hi all plz tell me difrence between analog or digital load cell.
Where do we consider the pressure in mbar & where do we consider the pressure in bar & why is it so ?
2 Answers BOC, Jindal Steel and Power,
How can test or measure the probe and extension cable to identify if the problem at the probe or cable or at the driver it self? (pleast notify the measuring method)
How would i calibrate a new commissioned flow transmitter???
If a flow transmitter (magnetic type FT) that can measure flow and temperature, then why in some industries people use flow transmitter and temperature transmitter in the same line 1 after another? Even after 1 single flow FT is capable of measuring flow as well as temperature.
1 Answers Process Control Technologies,
What are the uses of orifice plates?
can we use flow transmitter instead of level transmitter?
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)