Ok I think I understand what you are asking. In most SMART
transmitters you have a digital indication on the
transmitter and you want to change what is displayed on this
indicator. You also said that you have changes the unit of
measure inside the transmitter with the HART, and this also
changed the UOM that is displayed.
There is a different parameter that you need to modify to
change the display. The parameter is normally something like
"set disply" or something like that.
Be aware that it will only display UOM or percentage or
display a switching between the two. What ever you have set
your UOM to inside the transmitter, will be displayed on the
indicator as the UOM. You cannot set the UOM to mmH2O inside
the transmitter and then display mBar on the display.
Also note that for a level application this display is
normally set to percentage and not UOM. If the operator look
at it he needs to see % level and not mm level. In a
pressure, flow or temp applications you want this display to
indicate UOM again.
Good luck
Is This Answer Correct ? | 6 Yes | 2 No |
Answer / omer baosman
First of all,parameter's which need to be diagnostic in
transmitter with any of communicator will be in percentage .
Like for flow eg: Kgs,temp eg:cc fh level eg: % ,pressure
psi or bar.
Is This Answer Correct ? | 0 Yes | 1 No |
Why flow/pressure transmitter before control valve?
what is the input of conductivity sensor and meter during the calibration time and what is the output?
If you calibrate a pneumatic pressure transmitter, how many adjustments are normally necessary or mandatory?
In oil & gas industries and petrochemical industries, there are classification of zones like zone 0, zone 1, zone 2. Is there any differences in voltages or power supply supplied for the process instruments, control instruments depending on the zones
In thermocouple could we use the lug for termination or not,Thermocouple is any time,I am currently concerned with K type.please let me know if anybody know
4 Answers Saudi Aramco Shell Refinery Company SASREF,
What is the cascade control system and where is use in power plant give the detail with block diagram
What are the two states of a controller
Why DP level transmitter preferred for closed vessels and Radar level transmitter for open tanks??
how to calibrate mass flow meter (Coriolis)? Example calibration range: 0 to 2500 kg/hr line size 3" fluid: Etheline glycol (MEG)
Q- Control problem are mainly classified in _____ types. a-)4 b-)3 c-)6 d-)nono of these Few of them i know is 1- regulator type problem (eg- Air conditioner) 2- tracking problem (eg missile trcking problem) 3- sybernatics 4- optimal control problem
how can we calibate ph meter. how can we calibrat conductivimeter how can we calibrat massflowmeter & it s working.
why we use cascade control and feed forward control in 3 element drum level control measurement of steam drum .what is cascade and feed forward control system ?give example .