IS IT POSSIBLE TO CALIBRATE A LEVEL TRANSMITTER INDICATOR(ABB)
USING HART COMMUNICATOR.? I MEAN TO CHANGE FROM ONE UNIT TO
ANOTHER WITHIN INDICATOR (EG. INCH TO FEET)...? PLZ NOTE
THAT I HAVE MADE THE UNIT CHANGE IN TRANSMITTER USING HART
COMMUNICATOR..BUT WHAT ABOUT THE INDICATOR..?
Answers were Sorted based on User's Feedback
Ok I think I understand what you are asking. In most SMART
transmitters you have a digital indication on the
transmitter and you want to change what is displayed on this
indicator. You also said that you have changes the unit of
measure inside the transmitter with the HART, and this also
changed the UOM that is displayed.
There is a different parameter that you need to modify to
change the display. The parameter is normally something like
"set disply" or something like that.
Be aware that it will only display UOM or percentage or
display a switching between the two. What ever you have set
your UOM to inside the transmitter, will be displayed on the
indicator as the UOM. You cannot set the UOM to mmH2O inside
the transmitter and then display mBar on the display.
Also note that for a level application this display is
normally set to percentage and not UOM. If the operator look
at it he needs to see % level and not mm level. In a
pressure, flow or temp applications you want this display to
indicate UOM again.
Good luck
| Is This Answer Correct ? | 6 Yes | 2 No |
Answer / omer baosman
First of all,parameter's which need to be diagnostic in
transmitter with any of communicator will be in percentage .
Like for flow eg: Kgs,temp eg:cc fh level eg: % ,pressure
psi or bar.
| Is This Answer Correct ? | 0 Yes | 1 No |
give some question relative instrument fitter?
WHAT IS AN INTERLOCK SYSTEM ?? HOW THEY WORKs ?? WHERE IT IS USED ??? MAINLY ??
2 Answers TATA, Tata Steel Limited,
Type of level transmitter commnly used in Procees area are the following. a.________________This type of level transmitter works as follows
Which types of quections asked in interview for FORMULATION PLANT (PHARMA)
Why rtd out put is ohm how create the ohm
what is the difference between RTU & MTU in SCADA system?
What is BMS (Building Managment System)& is AHU / HVAC are in BMS.
hi friends,im an instrumentation and contol engg student,can u hlp me of suggsting barc written question paper,my id is roysuvaranjan@gmail.com, cel no.9563591747
Any Transmitter Range (Span value) start from 2?
Why we use negetive (-)voltage in vibration system
Why Current(Ampere) is chosen as Fundamental Quanties not Charge(coulomb) ?
Dear all... I have 1 0-400 duplex type RTD, I connected the A side to the temperature indicator and B side to the PLC panel, but when I have observed then found that The PLC side temp has the variation. and it was distub to other RTD temp also. so what can I do.
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)