Dear Sir,
we met a disaster with our 62.5 kva genset, after rewinding
we informed by our contract engg that due to return current
coming in neutral & impropper earthing this happend.
But after all set up & load balance we checked & found
again we have about 20 to 32 amp return current on neutral.
we have 12 airconditioner + 12 mini fridge on single phase
line.
Pl suggest any idea to solved this problem
Answers were Sorted based on User's Feedback
Answer / guru
Ground the neutral point of Genset and your problem will be
solved
Is This Answer Correct ? | 5 Yes | 0 No |
Answer / sheikh
I think imbalance load is main reason of this problem and cross current compensation instrument transformer should be installed on your common bus bar to prevent this loss
but balance load all of 3 phase eleminate the highest neutral current.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / rishabh sharma
i think the load on your single
phase need to be distributed to all
three phases equally. this problem
occures due to load imbalance.
Is This Answer Correct ? | 1 Yes | 1 No |
How would you supply power to a village which is very far from a sub-station and has only a 11k?
How to calculate the Efficiency of Chiller
how to calculate the power loss of cable?
depletion layer will form beforre biase or after bias ?
Auto transformer starter gives the same effect as star/delta strater if its turn ratio = A 0.5 B 0.67 C o.66 D 0.577
I have a generator of 300kw.400V,50hz . what is means can i assume the load Red Phase with Neutral 300kw.Yellow phase with neutral 300kw and Blue with neutral also 300Kw. or - red with neutral 100kw same as yelloe and blue phase also giving 100kw with neutral respectively
Please explain, how to test vector group of tranformer(Delta y1) . Thank
my UPS suddenly goes off and all panel light also blow off.This happens even main electric supply is not interrupted.After some time it automatically starts functioning normally.Batteries are new.
Hi everyone, I'm Lachuu, recently joined automation company as PLC Engineer. I have certain basic question, I request all big gurus and seniors to answer these question. Because this will be very helpful to me as well starters like me. How to design a control circuit (ex: pick & place - my current project) Yamaha robot PxYx series controller RCX222, using 6 cylinder double acting, plc keyence kv p16r 2 expansion unit for input and output each. How to select panel terminal mcb elcb powersupply. My main concern in some projects how to select dc power supply, mcb rcb(I came across dif bt b c d curves, but stil confusing, pls help me :-(. I would really appreciate all who are going respond to this question.
why motors are rated in hp?
show the physical connection and phasor diagrams of 1: DZO 2: Yd1 3: DZ6 4: Yd11 5: YZ11
What is auto changeover and how it works plz write details.