How Much Capacity of Diesel Genset is suitable for
20 no.s of 1.5ton AC's & Why?(Load Calculation)
Answers were Sorted based on User's Feedback
Answer / vivek sri
Lokesh Thota & Girijapati Mishra are partly correct
1.5 Tons=5.25KW (1Ton=3.5kW)
Assuming COP of 2.5 Input KW = 5.25/2.5=2.1kW
If the AC is rated for 240 volts then
I=(2.1*1000)/(240*0.8)=10.94 Amps where 0.8 is the power factor.
For 20 Ac's I=10.94*20=218.75
In case you are using single phase generator with rated
voltage of 240 volts then the required genset capacity is
=240*218.75/1000=52.5kVA.
In case you are using a 3 phase generator with voltage
rating of 415 volts (L-L, Line to neutral voltage will be
240 Volts) then rating would
be=1.732*415*218.75=157kVA(1.732 is SQRT 3)
Is This Answer Correct ? | 1 Yes | 6 No |
what is the internal fuction of a ceiling fan?
why we use end termination kit for ht xlpe cables
What is Plank's Law?
WHERE IS THE LIGHTING ARRESTER SHOULD BE PLACED IN DISTRIBUTION LINES?
What is the basic principal, by which DC voltage level is increased more than the supplied AC voltage during conversion. As upto AC level it is contorrled by firing anlge but after maximum level how is it possible.Please clear picture. OR we have to supply the higher level AC?
How to identify Motor leads in their order coming out from winding without tag (U1, V1, W1 & U2, V2, W2)?
how to calculate kA rating of device?
3 Answers Siemens, Vijai Electricals,
why is the earthing pin on 3 pin top are big and thick
what is the chemical reaction of solt and charcoal in earthing?
I BOUGHT A HAVELLS ACCL WITH GENERATOR STOP FASCILITY(i.e- BASICALLY IT IS A AUTO CHANGE OVER SWITCH) FOR MY HONDA EXK 2000S HOME GENERATOR (WHICH START IN PETROL & RUN IN KEROSENE). ACCL HAS 8 POINT. 2 FOR MAINS(PH & NUE), 2 FOR LOAD, 2 FOR GEN AND 2 FOR IGNITION POINT(X1 & X2). THE IGNITION POINT IS SPECIALLY FOR AUTO ENGINE STOP WHEN MAINS POWER RESTORE. I CONNECT THIS X1 & X2 POINT TO THE GENERATOR STATER MOTOR & EARTHING POINT. BUT WHEN MAINS FAILS THE GENERATOR COULD NOT START, BUT WHEN DISCONNECT THOSE X1 OR X2 POINT, THEN THE GENERATOR START. BUT WHEN MAINS ON THEN THE GENERATOR SHOULD START, AND WHEN I OFF THE MAINS THE GENERATOR AUTOMATICALLY STOP. PLESE HELP ME HOW I STOP THE GENERATOR AUTOMATICALLY WHEN THE MAINS RESTORE.
If we increase frequency in transmission line in lieu of voltage what will happen?
can you any one give exact mathematical relation between AC current and DC current?