Does RCCB do the job of MCB? Lets take 16A RCCB. it trips
when residual current exceeds 30mA. does it trip in an over
current situation, i.e when current exceeds 16A ??
Answers were Sorted based on User's Feedback
Answer / sivasankaran
Resuidal Current circuit breaker means it can sense only
the residual currents. But it does not have overload or
thermal protection.
Is This Answer Correct ? | 6 Yes | 0 No |
Answer / prashant
what u require is something which can do the job of
ELCB+MCB. U may use ELMCB or RCBO
Is This Answer Correct ? | 5 Yes | 2 No |
In dc motor starter there is less voltage required for holding contactor that's may why it is called no volt coil. but in ac starter why holding contactor is called no volt coil.
what is mean by xlpe swa pvc
suppose i have two single and three phase induction motor,thier have not any rating on its panel,anybody can tell me which motor is single or three phase?
33kv Rated output avilable in market (any where in india)
why we take movement of rotor always in counter-clockwise direction in 3-phase induction motors?
Will sag depends on the Specific Resistance of the conductor?if not Why??????????
In what condition the HT fuse breakes?
We have 2 Nos. Transformer with the capacity of 2000KVA and 1250 KVA and currently using only one 2000KVA T/R during operational hours while non- operational hous 1250 KVA T/R also used to reduce T & D losses. Similarly, 2 capacitor bank of 500KVAR and 300 KVAR also installed to balance reactive power. Now problem is around 1000 KW load PF is not maintaning 0.99 as 350 KVAR capacitor is in healty condtion. Now the PF is maintain 0.95 to 0.96.
What is DC power factor??
What is the use of mc( moving coil) in dc voltmeter and dc ammter and what is the use of ( moving iron)in ac voltmeter nd ac ammeter
What is rotor angle stability?
what is the difference between cable routing and scheduling?