Can HT cable(11kv cable) be used for 415V, 700A requirement.
Answers were Sorted based on User's Feedback
Answer / ashish baluni
Cable used for HT is designed for High Voltage and low
current carrying capacity. But for Low voltage rating
current requirment is very high which would cause Excess
heating in cable and will result in Puncturing of cable at
weak point.
For Ex- HT side Power=HT Vol* HT Current,if this cable
would be used for Low voltage then Power will be same. Thus
LT Power= HT Power
> 415*700 = 11000* I (Power factor is assumed to be unity)
> I= 26.5 Amp (For HT cable)
Thus,HT cable cant be used for Low voltage at High Current.
Is This Answer Correct ? | 16 Yes | 1 No |
Answer / v.senthilkumar
We can use HT cable for 415V, 700A. But you have not
mentioned any HT cable rating. If you mention HT cable
rating then we can analise whether it can be use or not.
Is This Answer Correct ? | 4 Yes | 2 No |
Answer / ranjit
Actually we cant use HT cables on 415 V LV side because of
without neutral cable. we can use HT cable with neutral
additionally. Neutral cable based on copper size which is
inside on HT cable. Because normally HT cable insulation
more less copper. because HT side High voltage less
current. But economic wise this is not good idea also.
Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mehul
we can't use h.t. cabel as l.t. cable.
because the cost of your h.t. cable is much higher han same
rating h.t. cable.
Is This Answer Correct ? | 2 Yes | 3 No |
Answer / mathew
normally, for HT we are using 240Sqmm cable in ring circuit. this 240sqmm cable is not sufficient for 700A, 2x240sqmm is sufficient for 700A. but we can use this 240 for both 11KV and 415V, thats not a problem.
Is This Answer Correct ? | 2 Yes | 5 No |
Why is the earth fault relay connected to the Yellow Phase?
Distinguish between neutral earthing and equipment earthing?
what is upper impedance and lower impedance of a distance relay
what is ten delta ?
what the purpose of data retrivala panel in substation
If 24 KVA AVR having Input voltage 200-400v, Output voltage 415+-1%, what will be the voltage if Load is 13A.
6.6 KV /.415KV Step down trf. we can get 6.6 KV from primary by applying .415 KV secondary side by same TRF.
Why? We r used 50sq. mm. And above size cable in 3.5 core and below size are used in 4core
The unit of resistivity is:(a) ohms(b) ohm millimetre(c) ohm metre(d) ohm/metre
Define the "All - Day Efficiency" of a Transformer
What is the importance of RESONANCE
why cant we use earth as neutral at home whereas neutral is actually grounded at transformer end?