Can HT cable(11kv cable) be used for 415V, 700A requirement.
Answers were Sorted based on User's Feedback
Answer / ashish baluni
Cable used for HT is designed for High Voltage and low
current carrying capacity. But for Low voltage rating
current requirment is very high which would cause Excess
heating in cable and will result in Puncturing of cable at
weak point.
For Ex- HT side Power=HT Vol* HT Current,if this cable
would be used for Low voltage then Power will be same. Thus
LT Power= HT Power
> 415*700 = 11000* I (Power factor is assumed to be unity)
> I= 26.5 Amp (For HT cable)
Thus,HT cable cant be used for Low voltage at High Current.
| Is This Answer Correct ? | 16 Yes | 1 No |
Answer / v.senthilkumar
We can use HT cable for 415V, 700A. But you have not
mentioned any HT cable rating. If you mention HT cable
rating then we can analise whether it can be use or not.
| Is This Answer Correct ? | 4 Yes | 2 No |
Answer / ranjit
Actually we cant use HT cables on 415 V LV side because of
without neutral cable. we can use HT cable with neutral
additionally. Neutral cable based on copper size which is
inside on HT cable. Because normally HT cable insulation
more less copper. because HT side High voltage less
current. But economic wise this is not good idea also.
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / mehul
we can't use h.t. cabel as l.t. cable.
because the cost of your h.t. cable is much higher han same
rating h.t. cable.
| Is This Answer Correct ? | 2 Yes | 3 No |
Answer / mathew
normally, for HT we are using 240Sqmm cable in ring circuit. this 240sqmm cable is not sufficient for 700A, 2x240sqmm is sufficient for 700A. but we can use this 240 for both 11KV and 415V, thats not a problem.
| Is This Answer Correct ? | 2 Yes | 5 No |
what is the natural resistance of the earth? and how it effected by rain r snow? wat is the natural resistance of wet soil? define natural resistance?
Difference between stepper motor & induction motor.
which cable is preferred PVC OR XLPE for voltage from 220V to 11 KV with proper justification
What are the necessary solutions needed to be carried out on a malfunctioned earthing mechanism of a VACUUM CIRCUIT BREAKER.(TAMCO)
An 8 pole, 50 Hz, 3-phase IM is loaded to a poing where pull out torque will occur. The rotor resistance per phase is 0.3 ohm and motor stalls at 650 rpm. The rotor frequency at maximum torque point is A 3.33% B 4.44% C 5.55% D 6.66%
what is the difference between star and delta connection?
how does it help for selection of a transformer.
will a transformer work when pulsating dc id applied to its primary?? what will be the result??
I have a 25kVA three phase transformer on our property. Will this transformer be large enough to run a large home with swimming pool, spa, 2 off full size reverse cycle air conditioners to service a 100 square house (10,000 square feet or 930 square metres)and the general power consumption of this house without upgrading to a 63kVA transformer.
what is the difference between 2phase & 3 phase?
For overhead protection we use which transformer?
What is Procedure the procedure to select CT's & PT's in 66kV and above substation?
3 Answers Infotech, Vijai Electricals,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)