I have a 25kVA three phase transformer on our property.
Will this transformer be large enough to run a large home
with swimming pool, spa, 2 off full size reverse cycle air
conditioners to service a 100 square house (10,000 square
feet or 930 square metres)and the general power consumption
of this house without upgrading to a 63kVA transformer.
Answer / s c budhiraja
Yes, this transformer is large enough for the house in
question.A normal house requires 100w/sq.meter area
including Air conditioning.The 930 Sq.meters reqire:9300w.
and add 10kw power reqired for the SPA. So total power
reqired is 19.3KW.A 25kva Transformer can supply power of
20kw at naormal power factor of 0.8. So the transformer is
is large enogh to meet the power requirement of the house
in consideration.
| Is This Answer Correct ? | 2 Yes | 0 No |
can transformer work on dc or not?if we increase the inductance of transformer can it happen to work on dc?
How can calculate HT side VCB? For example I have 1250 KVA load what will be HT side VCB Amp.range and what size XLPE cable I use for HT side.
2 Answers NASSA, Orchid, SB Automation,
3phase motor 400v (induction) A.C 4kw company design 1400rpm but our requirement 2000rpm possible? attached any instrument. reply fast! contact 03343262442
is tree is a good conductor and it may be used for conductor?
Q.1:What protection will be used on HT and LT side of 33/0.4 KV, MVA transformer. Indicate capacities of protective device to be used. Q.2:Which types of back-up protections are used in the power transformers? What do you understand by the term over travel in the relay? Q.3:How star and delta connected winding transformer are provided from earth fault
What is K-rated transformer? What is the use of it? What can be the size(pls provide calculation if possible) of K- factor transformer for 550kW,690V motor operating with drive (VFD)?
A single line diagram(SLD) and a purchase order of a 11/66kV switchyard of a power plant was given. In the SLD, only one lightning arrestor(LA) was shown, but the purchase order had need of 3 LAs. Is this correct, if yes, why?
what happened when we supply a dc current in dc motor?? can it worked properly?
i want to run 11kv star connected motor in 6.6kv with delta connected throught inverter, is it possible?
what is DG A,B,C,D check?
Why in Hv transmission line as we see there are generally 6 or more than 4 conductor wires are used instead of 4 i.e. 3 for phase and 1 for neutral wire?????
Before given the connection to Alternator (pre- commissioning) which tests we will conduct
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)