Answer / vijay shinde

transformer rating is in kva because iron losses are
depends on voltage of transformer and copper losses are
depends on current of transformer so its in kva

Is This Answer Correct ?    7 Yes 0 No

why transformer rated in KVA not in KW ? we know that W= v*i..

Answer / praveen420

rated transformer o/p is limited by heating and hence by the losses in transformer.mainly two type of losses occur in transformer iron loss and copper loss.iron loss depend on voltage and cu loss on current(amp)and these are almost unaffected by load pf so rating of transformer expp.in kva,va rather than kw.
w=v*i*cos(angle) in case of AC.
w=v*i in case of DC

Is This Answer Correct ?    5 Yes 1 No

why transformer rated in KVA not in KW ? we know that W= v*i..

Answer / kingshuk dey

This is one of the sure questions of graduate interviews. I'll try to explain it in the simplest possible manner , using least technical words and more "English". :D

KVA is the power available for use. KW is the power that is actually used. Transformer is a source of power and supplies to the motor (consumer of power).
KW=KVA *cos(phi).
This "cos (phi)" or power factor is the efficiency in which the electrical system is utilizing power. cos (phi) is 0.85, means the system is 85% efficient. The rest 15% power is being wasted as heat etc. This factor only comes to play when there is a complete system (producing power and consuming power).
Hence transformer is rated as KVA and motor KW (cos phi comes into play in KW to specify it's efficiency to use the KVA power generated).

Is This Answer Correct ?    1 Yes 0 No

why transformer rated in KVA not in KW ? we know that W= v*i..

Answer / lalgpt

Transformer rating is always on KVA that is
Kilo Volt Ampere Simply Volt ampere

but equation of power is VICos()

And the transformer has two losses one is copper loss
and the other is the core loss these two losses
are depending on current (I) and Voltage(V) only not
on Cos() that is why rating is in VA

Is This Answer Correct ?    0 Yes 0 No

why transformer rated in KVA not in KW ? we know that W= v*i..

Answer / pratheesh

Transformer is a power source(supplier) whicah can
deliver X amperes at rated voltage. So units of these
values are Voltag(V) and Current(I). It means all the
power delivering equipmets such as Transformers and
Generators are supplying I ampere at V voltage. Thats y
its rating is V*I == V*A

Power W= V*I cosQ.
Not V*I. (It is in DC)

Is This Answer Correct ?    3 Yes 4 No

why transformer rated in KVA not in KW ? we know that W= v*i..

Answer / guru

Transformer is mere equipment which transforms the voltage
and current as per the requirement. KW are rated for
equipments which converts electrical energy to other energy.

Transformer rating in KVA is due to it converts electrical
energy to electrical energy and all electrical ratings are
done only in voltage and current or combination of both,
like CB rating in Voltage and current, Bus bar rating in
amperes etc.

Is This Answer Correct ?    1 Yes 3 No

Post New Answer

More Electrical Engineering Interview Questions

what is the difference between old fan regulator and new fan regulator

1 Answers  


i am studying in final year can i allowed for 23rd UES of Indian army

0 Answers   TCS,


what type of earthing do for dry fissure rock?

0 Answers  


what happens when a dc shunt motor fed with an alternating suppy ?

1 Answers  


how works inductive &capacitive sensors?

0 Answers  






Why sometime AVR and sometime Booster coil is used in Alternator? what is the diferance between AVR & Booster coil due to which they are selected

0 Answers   Bajaj,


i had aplied Hindustan Petroleum corporation limited for the post of maintenance technician -Electrical,i want model questions,if anybody have please send it or please advice?

0 Answers  


What is the drawback of static coefficients?

0 Answers  


i am an maintenance engineer. one distribution board have 5 feeder. recently its ELR trips frequently, but it take some times after trip( 10min,20min..)but 3 feeder no load. two feeder only loaded. i checked one feeder IR value all values are above 50Mohm.but B phase to Earth is only 9Mohm.any problem about low value

0 Answers  


Why in metering Ct for ammeters ct secondary side is grounded for each Ct but not in case of CBCT (Core balance current transformer)..kindly some1 highlights the reason..is it because net flux is zero?

0 Answers  


What happen when increese more than 50HZ fequincy.

5 Answers  


What is effect of low pf on HT supply.

6 Answers  


Categories
  • Civil Engineering Interview Questions Civil Engineering (5085)
  • Mechanical Engineering Interview Questions Mechanical Engineering (4451)
  • Electrical Engineering Interview Questions Electrical Engineering (16632)
  • Electronics Communications Interview Questions Electronics Communications (3918)
  • Chemical Engineering Interview Questions Chemical Engineering (1095)
  • Aeronautical Engineering Interview Questions Aeronautical Engineering (239)
  • Bio Engineering Interview Questions Bio Engineering (96)
  • Metallurgy Interview Questions Metallurgy (361)
  • Industrial Engineering Interview Questions Industrial Engineering (259)
  • Instrumentation Interview Questions Instrumentation (3014)
  • Automobile Engineering Interview Questions Automobile Engineering (332)
  • Mechatronics Engineering Interview Questions Mechatronics Engineering (97)
  • Marine Engineering Interview Questions Marine Engineering (124)
  • Power Plant Engineering Interview Questions Power Plant Engineering (172)
  • Textile Engineering Interview Questions Textile Engineering (575)
  • Production Engineering Interview Questions Production Engineering (25)
  • Satellite Systems Engineering Interview Questions Satellite Systems Engineering (106)
  • Engineering AllOther Interview Questions Engineering AllOther (1379)