Answer / manoj sharma
It is very simple. You should first know the voltage rating
of your load supplied by UPS. Let it is X volt. Now you
have to decide which type of batteries you want to use
according to nature of your load and maintenance factors.
There are mainly Lead-acid battery, NI-Cd battery and VRLA
battery. If you use Lead-acid battery. A lead acid battery
has 2.2V/Cell standard. So Number of battey cells are X/2.2
for Laed acid battery. Now second thing is what is ampere
requirement for your load and for how much time. Let you
want 30 A current for 10 hours. Then capacity of your
single cell of battery must be 30*10 means 300AH.
| Is This Answer Correct ? | 7 Yes | 0 No |
Answer / nbs
that is depending on your back reqirment.you should metion
ups rating and how much time you need back, input voltage (
1 phase or 3 phase).
Hwre iam giving one example:
if you have Ups =5KVA
bacck ups requirent is = 2hr
batteries/battery capacity reqirement:
dischage current = 5000X 0.8
-----
0.9 X 12
=370.37 A
battery capacity = 370.37 X2 = 740.AH
you can take = 4 No.s x180 AH
total no.of batteries = four 180AH batteris
Note:
at dischage current , 0.9 inveter efficency
12v battery voltage
| Is This Answer Correct ? | 1 Yes | 0 No |
Answer / shamim ahmed
You Should Know the KVA rating of your UPS, time you want
to get Back-up & the Battery input voltage of your UPS.If
your UPS rating is X , time T and the UPS input voltage is
V then the Battery current capacity is:
I=X*T*1.25/V*0.7 AHr
suppose battery input voltage of your UPS is 36V and you
find the Battery capacity from calculation is 300Ahr.
then you can use 3pcs 12V 300AHr battery in series or you
can use 2pcs 36V 150AHr battery in parallel.
| Is This Answer Correct ? | 1 Yes | 1 No |
Explain the iniluencc of short circuit ratio on the pert'orniancc of synchronous machine.
Why only plate(copper) Earth pit given for neutral earthing? why not pipe(G.I) Earth pit?
Latching current is slightly less than ?
what curve and rateing would you use for a three phase 0.75kw motor?
what is the reasons for blowing fuse
Dear All we are having a problem in G120 BOP showing alarm A0503, F0052, F0060 we can not remove fault alarm ,Please any body help us. kowsar
What is the necessary and sufficient condition for stability.
what happens if power factor is maintained at 0.9?give me the answer in technicall way rather than telling the penality n all
Why can't we take NO LOAD TRIAL of motors having V1 mounting??
Where can I get CPWD electrical shedule rates in web? please help me.
Draw the vector diagram and condition for the following: 1) Dyn1 2) Ynd0 3) YnYn0
IF we have 500kva transformer 11.0/0.415V, 50Hz. How to calculate the current on HT & LT side, how can we consider for its breaker (HT & LT both)? You are requested to solve the question herewith.
3 Answers Bhutan Power Corporation,
Civil Engineering (5086)
Mechanical Engineering (4456)
Electrical Engineering (16639)
Electronics Communications (3918)
Chemical Engineering (1095)
Aeronautical Engineering (239)
Bio Engineering (96)
Metallurgy (361)
Industrial Engineering (259)
Instrumentation (3014)
Automobile Engineering (332)
Mechatronics Engineering (97)
Marine Engineering (124)
Power Plant Engineering (172)
Textile Engineering (575)
Production Engineering (25)
Satellite Systems Engineering (106)
Engineering AllOther (1379)